Hi

Is it acceptable to use the adiabatic equation to work out the size Main Earthing conductor to install in a standard domestic property for a consumer unit change.

Ive always been under the impression that its 25mm tails and 16mm main earth for a tns or tncs system, but a colleague thinks its acceptable to install a much smaller main earth as long as its ok by the equation.

Any help very much appreciated.
 
why bother with equations when it's so simple to bung in a couple of ft. of 16mm.
 
if you assume a TN-S with a Ze value of 0.8, then your pefc would be 300A assuming 240v. that's the minimum fault current flowing through that earth conductor. could be considerably more if Ze is ( as it usually is ) lower. that's why we all use 16mm.
 
  • Like
Reactions: 3 people
Hi

Is it acceptable to use the adiabatic equation to work out the size Main Earthing conductor to install in a standard domestic property for a consumer unit change.

Ive always been under the impression that its 25mm tails and 16mm main earth for a tns or tncs system, but a colleague thinks its acceptable to install a much smaller main earth as long as its ok by the equation.

Any help very much appreciated.

Your colleague is correct. It can be obtained by calculation or measurement.
 
why bother with equations when it's so simple to bung in a couple of ft. of 16mm.

Oh I dunno, how about to maintain certain levels of competence.
 
true, problem is, if say, by using the adiabatic equation, you quite correctly chose to use , say, 10mm, then along comes mr. clipboard ans says " that's no good, it's got to be 16mm." sometimes you just can't win.
 
true, problem is, if say, by using the adiabatic equation, you quite correctly chose to use , say, 10mm, then along comes mr. clipboard ans says " that's no good, it's got to be 16mm." sometimes you just can't win.

I can't argue with that. Happened a few times to me before, I took a white board to a building site once, embarrassed the hell out of him.
 
probably be 25mm in the amendment, just to confuse us more.
 
  • Like
Reactions: 1 person
Whole estates of 100's of houses built in the 90's onwards by reputable national buiilders under a NHBC buildmark have 10mm earthing conductors on 60A 1361 type 2's service heads marked with a pme label. Someone within their design teams must hold a firm belief that this is appropriate. I guess though that this will be discussed for ever more withopinion polarised and that I will be confused for evermore..
 
The Adiadatic equation should only be used for CPC calculations only. The BGB gives guidance on main earthing conductors and bonding conductor sizes that should always be followed.

Beware that this equation is only a small part of a cable calculation. If used incorrectly you may find that R1+R2 and Zs readings may be excessive.
 
Whole estates of 100's of houses built in the 90's onwards by reputable national buiilders under a NHBC buildmark have 10mm earthing conductors on 60A 1361 type 2's service heads marked with a pme label. Someone within their design teams must hold a firm belief that this is appropriate. I guess though that this will be discussed for ever more withopinion polarised and that I will be confused for evermore..

Maybe since then some of those houses have burnt down and they've had to reconsider?
 
I'm 99% sure that using the adiabatic equation on all types of 100A BS 88/1361s, the results given require only a 10mm earthing conductor to be used for any of them, hence why I very rarely fit 16mm earthing conductors for domestic work. I have a couple of 100m rolls of 10mm in my van at all times for bonding, I'm not gonna spend the extra money on anything larger than 10mm unless I have to.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Adiabatic Equation
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
45

Thread Tags

Advert

Thread statistics

Created
2glasseyes,
Last reply from
malcolmsanford,
Replies
45
Views
8,910

Advert