I am not an electrician but I am after a bit of advice. Would Ibe correct in thinking that a vehicle hook-up lead, used to keep the cooling units running when vans are parked up at its home base, should have the cable clamp on a plug should be on to the outer insulation and not onto the individual wires (earth, neutral and live) I do not think it is but would welcome any feedback and any reference to what regulations the lead/plug clamp might be under.
 
You are correct that the clamp should be on the insulation.
(and incidentally the 'earth' wire in the plug should be longer than the others, so it's the last to pull out in the event of the clamp failing)

How about BS7671 Chapter 13 "Fundamental Principles". Clause 134.1.4 :"Every electrical joint and connection shall be of proper construction as regards conductance, insulation, mechanical strength and protection."
 
You are correct that the clamp should be on the insulation.
(and incidentally the 'earth' wire in the plug should be longer than the others, so it's the last to pull out in the event of the clamp failing)

How about BS7671 Chapter 13 "Fundamental Principles". Clause 134.1.4 :"Every electrical joint and connection shall be of proper construction as regards conductance, insulation, mechanical strength and protection."
Thank you Avo Mk8. Let me just state that I am in no way going to do anything with the leads, I am not qualified, but I had reported the lead as not suitable after my daily van check and given it to a manager (it was labeled as not to be used by me), only to find the same lead back on the van two more times, a colleague also checked the lead and could see copper. I have been told that they are ok as a "qualified" member of staff had checked them which of course made me query the so-called qualification and how this person was possibly checking other equipment. As I am not qualified I thought it would be proper to seek advice to give me a bit more confidence to take this further and hopefully stop someone from getting hurt.
 
As above, yes. Clamping on the wires, or indeed if the wires (i.e. "primary insulation") are exposed outside of any equipment or plug, would fail an electrical or PAT inspection.

See also this example in the H&S guidance (page 3 of the PDF document):
Thank you pc1966 for this information. I have replied to an earlier reply with a bit more detail but very much appreciate your input.
 
Thank you pc1966 for this information. I have replied to an earlier reply with a bit more detail but very much appreciate your input.
You are quite right to be concerned and whoever told you it is OK is clearly not qualified and talking out of the wrong orifice.

That H&S guide clearly shows what is expected of a 13A plug and also covers more about the requirement for periodic inspection and testing of electrical equipment in any commercial or industrial environment.
 
There is a lot more about testing here:

The law in this respect is a bit odd, although such oddness also applies to fixed wiring rules. It does not mandate that you have to inspect and test, however it is a legal requirement to maintain a safe working environment. Realistically the only way to do so and to have evidence to back you up if there ever is a serious incident is to do periodic inspection & testing.

It used to be called PAT from "portable appliance testing" since fixed wiring is covered by the EICR (electrical installation condition report) but that resulted in things like fixed wall-mounted heaters, etc, not being inspected by either regime (not portable, not part of fixed wiring). So that has been replaced by the"In-Service Inspection and Testing of Electrical Equipment" guidance, or ISITEE which is a lot less memorable!
 
Some pictures would be great, we like pictures.

there may be other reasons why the cable and plug are not acceptable.

one that springs to mind is the temperature rating of the cable as it is below freezing overnight in most of the U.K. at the moment.
unless it is designed for low temperature operation it could be damaged by being flexed at low temperature.
 
Some pictures would be great, we like pictures.

there may be other reasons why the cable and plug are not acceptable.

one that springs to mind is the temperature rating of the cable as it is below freezing overnight in most of the U.K. at the moment.
unless it is designed for low temperature operation it could be damaged by being flexed at low temperature.
Just a few photos showing the problem
 

Attachments

  • 20210705_191817.jpg
    345.5 KB · Views: 16
  • 20210527_223652.jpg
    430 KB · Views: 16
  • van wires.jpg
    366.5 KB · Views: 16
^^^^ What he said. The sad thing is that it would take minutes to put those 32's back on properly! Also, SY cable (the one with the metalic sheath) isn't suitable for that purpose (even though I see it daily).
 
^^^^ What he said. The sad thing is that it would take minutes to put those 32's back on properly!
Exactly, not a hard job for anyone electrically competant.
Also, SY cable (the one with the metallic sheath) isn't suitable for that purpose (even though I see it daily).
Its an odd one, yes it looks macho but there are few cases where it actually makes sense. It is not up to the protection of SWA and (most importantly) not UV resistant, but you still need it glanded at one end to earth the metal braid.

The rubber H07RN-F style is a much better choice, tough yet flexible, UV resistant and also fairly resistant to common stuff you find on the floor of workshops, etc. Quite a few places also sell it be the metre so you can buy what you need in the size(s) needed for the job.

Edit: Also good for some cases is the "arctic" cable, flexible down to lowish temperatures and usually in bright colours so easy to spot on poorly lit floors, etc. For example:
 
Last edited:
Exactly, not a hard job for anyone electrically competant.

Its an odd one, yes it looks macho but there are few cases where it actually makes sense. It is not up to the protection of SWA and (most importantly) not UV resistant, but you still need it glanded at one end to earth the metal braid.

The rubber H07RN-F style is a much better choice, tough yet flexible, UV resistant and also fairly resistant to common stuff you find on the floor of workshops, etc. Quite a few places also sell it be the metre so you can buy what you need in the size(s) needed for the job.

Edit: Also good for some cases is the "arctic" cable, flexible down to lowish temperatures and usually in bright colours so easy to spot on poorly lit floors, etc. For example:
BS7909 is based around use of H07 for it's mechanical properties. As essentially a rubber cable it's elastic nature makes it superior for dealing with knocks and abrasions, pulling etc. Arctic cable is frowned upon, not because it's particularly bad but because it's still a PVC cable and easily abraded and cut. SY cable has no advantage whatsoever in this application and can give users a false sense of 'robustness' that simply doesn't exist. The braid is designed for signal shielding, not mechanical strength.
 
Arctic cable is frowned upon, not because it's particularly bad but because it's still a PVC cable and easily abraded and cut.
That is useful to know. I see it used quite a bit but ceratinly the rubber stuff seems to survive better. Shame the don't make a coloured version!
SY cable has no advantage whatsoever in this application and can give users a false sense of 'robustness' that simply doesn't exist. The braid is designed for signal shielding, not mechanical strength.
We use a def-stan cable with copper braid for the EMC aspect, but that is fixed not flexible use, and not carrying mains power as such (though some of the lines are direct off mains via rectifier / thyristor bridge).

So far not found a genuine use-case for SY!
 
Shame the don't make a coloured version!
This has been explored! The black colour is part of it's intrinsic UV protection qualities. I'm also a fan of H07 for industrial installation environments as an alternative to Hi-Tuff or SWA (depending on methods etc, obviously) due to being far easier to work with in limited space, bend radius etc.

The last time I found a legit use for SY was when after having finished a nice neat install on tray, all dressed off, the wet-pants team suddenly realised they'd forgotten about a whole load of ELV sensors and control that needed running around - so had to squeeze some multicore DC stuff onto the same tray as all the 3ph.
 
This has been explored! The black colour is part of it's intrinsic UV protection qualities.
Ah, I had suspected that.
I'm also a fan of H07 for industrial installation environments as an alternative to Hi-Tuff or SWA (depending on methods etc, obviously) due to being far easier to work with in limited space, bend radius etc.
Good point, we use it for new with our floodlights on temporary fencing, though might get replaced with Flexishiled eventually.

I also try and use tri-rated for internal wiring when possible for similar reasons!
 

Reply to Advice about safety please. in the Auto Electrician Forum area at ElectriciansForums.net

Similar Threads

I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
939
Hi first time on this forum and looking for some advice. I have a second home with incoming network connection as shown below. I don't like...
Replies
1
Views
817
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
732
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
508
Hi, I’m new to the forum and am seeking some advice please. I’ve picked up a job that another electrician has abandoned, the job is to...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock