Hi, before taking my am2 I read some very helpful threads from this site. So anyone reading this also preparing I hope this helps I got through my install and testing fine. However I failed the fault finding C2. passed C1. Whatever that means. I did all my tests at the board and struggled on ring final. I have okay knowledge on rings, eg. end to end, figure 8 and insulation resistance. any help and advice for my re sit be great! thanks in advance
You say you failed fault finding but describe not fully grasping testing? These are two separate sections of the test. Which one did you fail?
Sorry for not being very clear. I passed the testing part live and sheets. I failed fault finding, I grasp my dead tests fairly clearly. The reason I mention the ring final circuits because I did end to end at the board and figure of 8. Went to every socket and they all read back roughly half the end to ends or r1+ rn divided by 4 ect. but couldn't find anything.
Erm I think so, Do you confirm polarity by the figure of 8 and if the reading is 1/4 of the R1, RN at every socket. If so yes, I done all ends to ends also
I think so, I did figure of 8 and the readings was all similar. and 1/4 of the r1 plus rN. I also had a question asking why when a customer touches the motor case and bonding clamp she feels a tingerling feeling. I tested one the bonding clamps was at 2 ohms something. So i presumed that was a high resistant joint. struggled to answer why the tingling feeling though!
That doesn't ring any bells with me dude. From what I can remember, you are looking for:
1. Negligible impedence (short) but it's important to use the correct terminology.
2. Open circuit.
3. Continuity.
You are only given a multimeter, so not testing IR or any live testing. Only so much you can do with a multimeter. The faults (8 in total) are described and simulated (as you know). All you can do is test with the multimeter, diagnose any of the 3 possible scenarios then state what you would do to overcome the problem.
I passed the fault finding, but failed the testing due to being under pressure I failed to disconnect the bonding before testing Ze (apparently). That's what they said anyway unless they were trying to fleece me for the extra £200 to resit that part. They also said i did something weird with the end to ends or figure 8, but were unable to expand on that but what do you say when they hold the 'pass' certificate?
HTH
Voltz
Also, with the tests results at the socket outlets I needed to explain the theory because the anomalous test results I achieved were so varied due to the nakkered state of the outlets.
i know what your saying.
im lucky just one clip on a breaker is missing. another lad had bigger problems.
all the terminals look like an ape has been at them with not one rounded screw (good think i have a pz/sl and multiple sl drivers)
Thanks for the advice man. I did my am2 at Harlow, I get a free resit on the smaller sub cats. And yeah it sounds right because parallel paths with when testing the ze. Also they want to make sure you reconnect the main earth! Because the resit is free I just ordered guidance note 3. Going to just go through all the dead tests for whatever circuit it is. I must find it that way.
Reply to Am2 advice! in the UK Electrical Forum area at ElectriciansForums.net
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
I just done my am2s flew though my testing but filled one box wrong on test cert will that be a fail ?