So the SFCU is the spur, protecting a 2gang socket?
Yes
Discuss Am2 socket circuit help!! in the UK Electrical Forum area at ElectriciansForums.net
So the SFCU is the spur, protecting a 2gang socket?
I wonder what an incorrectly rated 13A fuse is.Hi Adam, this description from a student begins with "read the instructions because they may change" but here it is :
View attachment 43639
There is your 1st mistake it's not a Ring Main, it's a Ring Final circuit11 12 and 13 is a ring main. 14 is a spur
Yes it is old Mate, but trainees need to understand circuit designation. things like calling a RFC a ring main, might be just enough to tip the balance in the examiners thought process, just saying.There is your 1st mistake it's not a Ring Main, it's a Ring Final circuit
Yep, it counts.....just like the 240v brigade.Yes it is old Mate, but trainees need to understand circuit designation. things like calling a RFC a ring main, might be just enough to tip the balance in the examiners thought process, just saying.
one from poundworldI wonder what an incorrectly rated 13A fuse is.
I did this today and wired it the same? Is that the diagram on the spec as I didn’t check either WHAT DID U ACTUALLY FAIL ON.Hi. I've got a resit for the Am2 in a month as I failed the socket circuit. The problem is, I'm not sure how ! I've drawn a quick diagram of the wiring they give you and how I would wire it.
The top drawing is the diagram they give you..
View attachment 43630
Not if its wired in 4mm2 that will be a 32Amp Radial Appendix 15 BS7671The clue must be in the breaker they give you....if its a 32 then ring it, 20 or 16 then radial
It’s a 32A rcbo it’s defo a ring wired in 2.5mmNot if its wired in 4mm2 that will be a 32Amp Radial Appendix 15 BS7671
The exterior socket IIRC is fed from a SFCU so should be a radial spur protected by a 13 amp fuse. Also the RFC was wired in 2.5/1.5 singles?I did this today and wired it the same? Is that the diagram on the spec as I didn’t check either WHAT DID U ACTUALLY FAIL ON.
I was responding to the post Whereby the poster said it it's a 32 Amp mcb then it's a ring, Radials will be 20 or 16 Amps which is misleading. If it says wired in 2.5mm2 and the OCPD is 32A then you are right An RFC Ring Final Circuit.It’s a 32A rcbo it’s defo a ring wired in 2.5mm
No probs with that MateSorry my friend new to this lol