Good work Damian, this amendment really is a load of BS....!

At a slightly different angle, what if a plastic CU that is deemed combustible is installed after 2016 upon the proviso it will be being housed in a fire rated/non combustible enclosure. Do we need to have the enclosure installed first... Bit of the old chicken and egg going on. Are we expected to be buying steel shells to house them.

Thank you.

To answer your question, if a plastic board is classed as combustible then it won't have passed the 960°C glow - wire test in accordance with BS EN 60695-2-10&11 as is required by BS EN 61439-3, therefore it won't meet the requirements of the product standard and should not be sold on the European market.

By definition, any plastic board that truly meets the current requirements of BS EN 61439-3 will be non-combustible.
 
Remember those stories of the 1st world war.
When the powers to be sat around a table smoking fat cigars and deciding on their strategy for the next attack.
Then they send thousands of lads, over the trenches to be mowed down by german machine guns.

Keep yer heads down lads, cus they sure don't give a ---- about the implications to us.
 
Sorry Damian, I skim read parts of this thread. But get exactly your point re 61439 DBs. This will rumble and rumble I feel!
 
Remember those stories of the 1st world war.
When the powers to be sat around a table smoking fat cigars and deciding on their strategy for the next attack.
Then they send thousands of lads, over the trenches to be mowed down by german machine guns.

Keep yer heads down lads, cus they sure don't give a ---- about the implications to us.

Very true, however in this scenario there is no implication to us. We can carry on fitting plastic boards as long as we want. BS 7671, in particular Regulation 421.1.201 only goes to bolster this point by referring us back to the product standard that defines non-combustible in the first place lol!

We've all been caught, hook, line and sinker by nothing but a red herring.

To those of you reading this who don't have a clue what we're all on about;

THERE IS NO REQUIREMENT AFTER 1ST JANUARY 2016 TO ONLY FIT METAL BOARDS IN DWELLINGS

:)
 
Thank you.

To answer your question, if a plastic board is classed as combustible then it won't have passed the 960°C glow - wire test in accordance with BS EN 60695-2-10&11 as is required by BS EN 61439-3, therefore it won't meet the requirements of the product standard and should not be sold on the European market.

By definition, any plastic board that truly meets the current requirements of BS EN 61439-3 will be non-combustible.

But they do play with words Skelt, as said the board I referred to is deemed Self-extinguishing.
Where does that stand with reference to Self-extinguishing vs Non-combustible.
Is there any official clarification on any difference or does it mean the same thing.
Or are they just going to sit back and leave the man on the tools to take the responsibility, and decision. ????
 
Maybe a product recall is in order. That could be a profitable little number.. In my dreams that is!
 
But they do play with words Skelt, as said the board I referred to is deemed Self-extinguishing.
Where does that stand with reference to Self-extinguishing vs Non-combustible.
Is there any official clarification on any difference or does it mean the same thing.
Or are they just going to sit back and leave the man on the tools to take the responsibility, and decision. ????

If something self extinguishes, by definition it cannot ignite. Ignition is the state of undergoing combustion. If it cannot ignite, then it is not combustible.

The company that produces the board can call it what they like. They can say that it is "rated at fifteen bananas on the Keanu Reeves scale", and so long as it passes the 960° glow-wire test, then it cannot be combustible.
 
If something self extinguishes, by definition it cannot ignite. Ignition is the state of undergoing combustion. If it cannot ignite, then it is not combustible.

The company that produces the board can call it what they like. They can say that it is "rated at fifteen bananas on the Keanu Reeves scale", and so long as it passes the 960° glow-wire test, then it cannot be combustible.
Don't you just love semantics
 
So,
Quote 1,
Consumer units and similar switchgear assemblies will have to comply with the BS EN 61439-3 standard.
And most of them already do !!
Quote 2,
An example of non-combustible material is steel.
But they DON'T mention plastic in that statement,even though its capable of being non combustible, and therefore starting the mythology !!

:icon12:

 
Excellent post Mr Skelton. I am glad someone (you) has been ar3ed enough to actually look at the regs regarding this farse!!!

This is one of the best post in a LONG time on this forum. I have copied your post and gave a copy to a few of my colleagues.

The BS7671 makes reference to conforming to the "manufacturers instructions" for any accesssory/equipment, therefore if the manufacturers state that their board conforms to BS 61439-3, then it is perfectly acceptable.


Jay
 

Reply to AMD 3 - Hopefully busting the myth of metal DBs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
460
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K
Many will by now have heard of the new requirements for private landlords, enacted under Statutory Instrument 2020 No. 312, known as ‘The...
Replies
48
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock