Good work Damian, this amendment really is a load of BS....!
At a slightly different angle, what if a plastic CU that is deemed combustible is installed after 2016 upon the proviso it will be being housed in a fire rated/non combustible enclosure. Do we need to have the enclosure installed first... Bit of the old chicken and egg going on. Are we expected to be buying steel shells to house them.
Thank you.
To answer your question, if a plastic board is classed as combustible then it won't have passed the 960°C glow - wire test in accordance with BS EN 60695-2-10&11 as is required by BS EN 61439-3, therefore it won't meet the requirements of the product standard and should not be sold on the European market.
By definition, any plastic board that truly meets the current requirements of BS EN 61439-3 will be non-combustible.