ABerry82

i have been asked to install a garage unit in a outbuilding they wanted a couple of sockets and lights and i think i allowed about 20A total output for design current. what size cable do you think bearing in mind its a 90 meter run in a trench from house to out building.i allowed 16mm does this sound like overkill
 
How much are you charging for that 90m 500/600mm deep trench?? Got to be worth hiring a mini digger for that sort of distance...lol!!
 
the 90m was her estimate. i did go to neweys to get a quote for both 16mm an 10mm swa. but i think i will go round and measure up for my self as swa isn't cheap
 
Rather than asking us, do your cable calcs tell you this will be ok? If they do it'll be fine, if not then pick the appropriate size
 
  • Like
Reactions: 2 people
Are you suggesting 16mm on a rule of thumb or have you calculated it taking vd into account? It may seem overkill but a 5% or 11.5 volt drop on a 230v single phase supply from supply cutout to your outbuilding will require an apparently large cable. I would normally design a sub-main vd calc on 2.5 to 3% so you can have allowance of around the same on your final circuits. Enjoy!
 
why have you allowed 20A?.....assume your going to use a 16A MCB...for the outlets....and a 6A MCB for the lighting......thats 22A mate.....
 
  • Like
Reactions: 1 person
16mm is the smallest i would use as that is 5.04 vd and max for lights is 6.9 so 10mm will be over this
 
What type of "Garage"? If its one you park cars in then fair enough, but the 90M walk to the house in a winters nights is a bit of a nightmare. In fact a nightmare at most times. 20Amp probably enough there, its not like they will be putting tumble dryers or washing machines in it that far from the house.

If it's a garage to work on cars/projects etc then 20Amp may be shy, could be the likes of a welder going in. I'd visit site, get a proper spec of what is going to be used out there and a proper distance from the house. Customer estimates on distances and the like tend to be well off and there is no point in wasting your own time sizing and pricing up cable until you know what you need.
 
why have you allowed 20A?.....assume your going to use a 16A MCB...for the outlets....and a 6A MCB for the lighting......thats 22A mate.....
but that's the MCB ratings, not the design current. would need a lot of lights to pull 6A.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Another cable sizing question
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
ABerry82,
Last reply from
Octopus,
Replies
15
Views
1,979

Advert