Back again with another problem and I had great help from my last Thread.
I am currently working in Spain and have a problem on a caravan site. There is a mains board installed in between 20 caravans which supplies each caravan. In the mains board there is a 20amp Circuit Breaker and an RCCD feeding each Van. The cables are in tube 3 x 6mm. Once into the van it feeds a fuseboard, In the fuseboard are all the circuits for the van all proteced by another RCCD in that board.

6 of the vans keep tripping their own individual RCCD in the outside board. Never does the internal one trip out. On 1 van i replaced the cables from the box to the van 10 metres and the problem is still there. I have tested all cables and have a reading of >999.

Very starnge ther other day at 0800hrs one resident went to switch her RCCD back on in the outside box and was met by another man doing exactly the same. They tripped out at the same time. This was not the first time either.

We do know that the voltage here is not as stable as the uk it varies from 200v to 250v.
I did remove the RCCD in the outdoor box for 2 weeks and the internal one did not trip out once. I have now reconnected it and its tripping again.

The RCCDS are GE 30ma 40amp.
I just can not come up with any more ideas
Hope someone can help.
 
Well it sounds like you have 2 RCD's in series. As in one protecting the cable to the caravan and 1 in the fuseboard in the caravan. This is not needed and will cause nuisance tripping.
Either take the RCD out of the CU in the caravan or for ease of resetting for the people if it trips, remove the 1 from the main CU. Is it SWA going to the caravans??
 
Spanish rules here says you must have an RCCD in the van and an RCCD at the source. The site will not allow me to remove the one outside. SWA is not used here, so the mains are in metal flexi tube. I do agree about 2 RCDs in series but if i remove the one in the van then the one outside may still trip out.


Well it sounds like you have 2 RCD's in series. As in one protecting the cable to the caravan and 1 in the fuseboard in the caravan. This is not needed and will cause nuisance tripping.
Either take the RCD out of the CU in the caravan or for ease of resetting for the people if it trips, remove the 1 from the main CU. Is it SWA going to the caravans??
 
This is something I came up with but when I asked our Spanish Engineer if we could, we were told that it does not comply with Spanish Regulations. Fighting a loosing battle in Spain
Well if they are the same rated RCDs then you have no discrimination. Can you not fit a time delayed RCD at the source?
 
Are the vans on TT out there???

Have you tried a ramp test to establish the tripping current of both RCD's, also a mA clamp meter to detect any earth leakage present???
 
We are limited to what testers we have here. We do nt have either of these testers
Are the vans on TT out there???

Have you tried a ramp test to establish the tripping current of both RCD's, also a mA clamp meter to detect any earth leakage present???
 

Reply to Another RCCD Tripping in the Australia area at ElectriciansForums.net

Similar Threads

DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
387
My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
864
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock