Hi,

I'd like to replace one of the breakers on an older Wylex board with an equivalent RCD. The current breakers are NB series "Type 2". If anyone knows IF I can find 20 or 25 amp RCDs that would fit and that are not wider than 2 standard breakers, and then of course, WHERE, that would be great.
Thanks,
MidAtlantian
 
Do you mean rcbo or rcd?

Sorry for the delay in responding. I just noticed your reply. Actually either RCBO or RCD would be OK. I've looked - including the web and Ebay. I can find the 63 and 100 amp RCDs - even if they take a lot of board space. But I have not seen 15 or 20 amps, and really I am not sure they were ever produced.

Cheers,
MidAtlantian
 
what i9s the need for RCD. is it for a new circuit ? if so could you not come off MCB in the CU to a RCD in an enclosure, then connect circuit into the RCD.?
 
You said that you want to replace one of the breakers. What you need is an RCBO.
Are you an electrician?
 
Yes, thanks. Space is tight, but that might be the only way to go. But! Can I add an "external" RCD without having to upgrade the main CU, since the new specs are for 30ma RCD on all circuits, and the old board has 100ma. I know it is safe enough, but is there are work-around on the "rules" side? I mean, it would not exactly be something you could miss.

Cheers,
 
Are you assuming the 63A RCD will trip on overload >63 amps? Is this why you were looking for a 25A RCD? Daz
 
DPG, Well, yes, I am assuming a 63A RCD would trip on 63A or an earth leak. That is for a zone of several "subordinate" breakers. For a single 2.5mm run to an external socket, I need a 20 amp breaker.

My question was about **availability** for an older Wylex CU. No one seems to have noticed that!

Cheers,
 
Thanks. Yes, it looks like a fused RCD spur was the answer. Its cuts the maximum power from 20 amps to 13, but that should be more than sufficient for this application.
 
Thanks. Yes, it looks like a fused RCD spur was the answer. Its cuts the maximum power from 20 amps to 13, but that should be more than sufficient for this application.

RCD's DO NOT trip on overload. The rating is purely the rated current which they can carry.

I'm always amazed at how many people do not know the basics of how their equipment works!
 
  • Like
Reactions: 2 people
RCD's DO NOT trip on overload. The rating is purely the rated current which they can carry.

I'm always amazed at how many people do not know the basics of how their equipment works!
its almost beyond words innit G......lol..
to the O/P:
get an electrician in to look at it....
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Availability of RCD for older wylex distribution board
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
MidAtlantian,
Last reply from
GLENNSPARK,
Replies
13
Views
3,397

Advert