in the event of a short circuit a massive fault current will flow.
the breaking capacity of a protetive device must be capable of interupting the fault current.
Most domestic mcbs are 6000 amp, some 10000.
indicated in a box on the mcb.
 
Thanks thats exactly what i needed, so it's marked on the mcb :) sorry to be a pain but im not one for doing test and putting numbers in boxes without knowing exactly what to check the result against.

Just getting as much knowledge as I can before doing my 17th
 
Thanks thats exactly what i needed, so it's marked on the mcb :) sorry to be a pain but im not one for doing test and putting numbers in boxes without knowing exactly what to check the result against.

Just getting as much knowledge as I can before doing my 17th


Read osg page 57 or GN3 pages 52 & 53 for examples
 
Protective device at origin of installation, is what? what is classed as origin

Outside in the street would be a local transformer on the output of that transformer would be connected a 3 phase supply which singlephase would be taken off to supply each house as the cable enter the house it terminated in to a REC service head which will have either an 80A or 100A BS1361 or BS88 fuse, from this fuse will doulble insulated 16mm or 25mm tails to the electricity supplier metering from the metering double insulated single core cable feed a CCU. I believe The origin is the first protective device belonging to you the householder as installed in the CCU, but it could be the REC cut-out
 
Table 2.4 in the Guidance notes doesnt mention an RCD ?????? what is the first protective device on a 17th edition compliance CU it cant be the main switch.

No rcd are not installed to provide protection against PFC, the electricity suppliers fuse and the MCB will provide protection against PFC (Fault L-N)

The RCD are their to detect earth faults (L-E or N-E) all RCD have a rated short circuit capacity of about 1kA only.

So when you are performing PFC testing the rated short circuit capacity of both the supplier fuse and your fuse/ circuit breakers installed in your CCU should be capable of disconnecting this current under L-N fault condition, not the RCD.
 
Outside in the street would be a local transformer on the output of that transformer would be connected a 3 phase supply which singlephase would be taken off to supply each house as the cable enter the house it terminated in to a REC service head which will have either an 80A or 100A BS1361 or BS88 fuse, from this fuse will doulble insulated 16mm or 25mm tails to the electricity supplier metering from the metering double insulated single core cable feed a CCU. I believe The origin is the first protective device belonging to you the householder as installed in the CCU, but it could be the REC cut-out

Good generic description for you by Zupos, but bear in mind not all installations will be upto recent specs included here - tails may be smaller, may feed more than one CU or you may find a 60A cut-out (common on bungalows etc)

The origin would be considered as at the DNO`s main (cut-out) fuse. All before that is regarded external to the installation (Suppliers equip / Ze) whilst all downstream is internal part (Consumers / R1+R2)

my understanding is the breaking capacity id the maximum fault current the mcb will take and still be able to be reset.

Icn = SC rating of protective device (marked in amps, in the little box) Fault current it can safely withstand without exploding/welding contacts etc - would not be expected to be usable afterward

Ics = service rating (the other single digit representing KA) same as above but the fault current it can withstand but still be serviceable after being reset

:cool: Cheers
 
Last edited by a moderator:
When using an instrument, what exactly is it measuring? I assume the resistance of the fault path, is this measurement taken at the incoming supply terminals with the CU main isolator closed (live).
 
When using an instrument, what exactly is it measuring? I assume the resistance of the fault path, is this measurement taken at the incoming supply terminals with the CU main isolator closed (live).

You`ve got it. Max fault current is the inverse of the loop. So it reads resistance of the loop, then divides into the measured voltage to derive PFC.

Basic Ohms... PEFC = Uo/Ze & PSCC = Uo/Zln

therefore Ze = Uo/PEFC & Zln = Uo/PSCC

The readings should be ideally taken as close to the meter as possible - for PEFC take phase from incomer (isolator open) & Earth from MET (or earthing bar/ link at supply cable)
Obviously, the PSCC measure would be taken between L & N (for single phase) at supply side of main switch.

Hope that helps :)
 
Last edited by a moderator:
So using a 3 wire test, two of the wires would be to measure the voltage and the third to measure the resistance of the earth loop? is the main incoming earth removed from the earth bar for this test; and croc clipped to measure impedance of the earth path back to the supply transformer,

Surely the possible size of current that can be drawn prior to disconnection is determined mainly by time, and this will be determined by the protection device installed by the supply company, anything from a 60 to100A cartridge fuse

how can a test instrument get a measure of this,
 
So using a 3 wire test, two of the wires would be to measure the voltage and the third to measure the resistance of the earth loop? [/qoute]

No, Richard. If using a 3 wire test meter then the usual procedure would be to connect the green & black crocs together, effectively making it a 2 wire tester for PFC (but check out user instructions for exact meter) Then, it`s as described above for 2 wires...

is the main incoming earth removed from the earth bar for this test; and croc clipped to measure impedance of the earth path back to the supply transformer
Again, no my friend, for PFC readings the earthing/bonding should all be in place. We`re trying to establish the maximum fault currents that could effect operation of protective devices & ensure that they`re upto the job (despite the content of the `other` post on this subject :confused:)
Be clear - we need the install to be as it would be under fault conditions - so as it would be in normal operation before the fault occurs. This would necessitate leaving the earthinng/ bonding in place when measuring, as the `normally` available parallel paths would induce a greater Earth Fault current, & it`s this `maximum` current we need to measure.

It`s perfectly fine (often more convenient) to croc clip to earthing bar to take PEFC - sorry if my previous post misled you on that - i`ve amended it

Surely the possible size of current that can be drawn prior to disconnection is determined mainly by time, and this will be determined by the protection device installed by the supply company, anything from a 60 to100A cartridge fuse

how can a test instrument get a measure of this,

You`re half right on that one. The cut-out fuse is there to do as you say. Trouble is, that fuse has it`s limitations - too much current drawn & it could disintegrate, explode or otherwise fail to interrupt the fault current - exactly what we don`t want after dutifully doing all we can to encourage the fault current to flow thru the install :eek:

So it`s critical we establish that the largest possible fault current that could be supplied is not greater than the protective device(s) can safely handle. Hence our measurement of the impedance of the fault path & the following calculation to estimate PFC :)
 
ok so the installation is left in its normal state energised, the bit that confuses me is 2 readings are taken and the highest recorded, what terminals are the two readings taken from.

Phase to Neutral followed by phase to earth and the larger of the two readings recorded,
 
Last edited by a moderator:
ok so the installation is left in its normal state energised, the bit that confuses me is 2 readings are taken and the highest recorded, what terminals are the two readings taken from.

Phase to Neutral followed by phase to earth and the larger of the two readings recorded,

P-N = PFC Readings taken between Phase - Neutral on incoming terminals of main switch
P-E= PEFC Readings taken between Phase terminal of main switch and earth bar in the cu.

On a TNS and TT you will get two different values of which the highest should be recorded.

On a TNCS both readings should normally be the same or thereabouts.
 
Yep got that the test is clear now, what is the state of the main CU isolator during the test

I switch off all cbs or remove fuses then switch off the double pole main switch and lock it off, before I remove the main earth to measure Ze, then reconnect earth measure Pefc (L-E) and then finally PSCC (L-N) only then do I remove lock switch on main switch, then each cb/fuse.
 
I switch off all cbs or remove fuses then switch off the double pole main switch and lock it off, before I remove the main earth to measure Ze, then reconnect earth measure Pefc (L-E) and then finally PSCC (L-N) only then do I remove lock switch on main switch, then each cb/fuse.

That would be the textbook way.

Not saying i always lock off when i`m stood at the board, but no-one could fault this approach.

But equally it can be done with all live - just frowned upon by EAWR :(

Very bad Saveloy :D
 
hang on you are both saying different things one has an open DP switch the other has it closed

Different person do it different ways, some inspectors just switch off c.b or remove the fuses and connect 3 lead tester to the bar live busbar, neutral busbar and earth/cpc busbar, I do not, I prefer to switch the main switch off as previously stated.
 
Its nothing to do with risk Im wondering about the low readings through lamps

Richard. Lamps don`t come into it. You are measuring the loop impedance of the L to N & the L to E fault paths external to the installation, then the meter calculates for you what fault current could be produced. Internal loads connected have no bearing on that whatsoever.

I think you need to re-read what has been written & have a deeper think about it.
 
Then just how would you be able to take a PSCC with the install isolated? That is the approved procedure.

I don`t think you could have read my last post mate. I explicitly said the loops being measured was external to the installation - that is, from point of measurement (supply side of incomer) to supply transformer & back again

Please.
 
Then just how would you be able to take a PSCC with the install isolated? That is the approved procedure.

By isolated I dont mean with the main incoming fuse removed im talking about the DP isolater in the CU, there is no hard and fast rule as to the state of this switch during the test?

page 57 fig 8 of GN3 shows load open circuit
 
Last edited by a moderator:
Yes I realise that, my question is if the switch was closed would it impact the reading, sorry if Im being padantic but I like to FULLY understand things :)
 
Yes I realise that, my question is if the switch was closed would it impact the reading, sorry if Im being padantic but I like to FULLY understand things :)

No because the cb/fuses in CCU should be switched/off removed, even if the main switch is on, or as you asked it may effect the reading.
 
It's just that I know adding load alters impedance, basic principle so it needs to be taken out of the equation for the external loop measurement, not clearly stated on the guidance notes.
 
Last edited by a moderator:
It makes no difference as long as the final circuit breakers/fuses are open circuit, if they are closed when the test is done then don't mesh characteristics come into play?

Its just that guidance note 3 does not make it clear and you would think it would.
 
As ElectricAL previously stated it would not matter, if you possess an ELZ/ PFC tester are are feel comptent to do so, go and test your own property with the supply on and supply off.

It great wanting to know every thing, but we are practical electricians, may be you should address this question to IET blog or IEEE etc.

I do know that my ELZ/PFC tester has an operating tolerance of +/- 20%, so if the meter not that accurate, then I do not think they are to worried about about any errors due to mesh loading.

I recently learned that for supplies upto 100A and protected by BS1361 type II as long as your measured value does not exceed 16kA and the CCU complies with BS 60439-3, then the installation will comply, so do not worry, get out there and as I previously said if competent get testing.
 

Reply to Breaking capacity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
331
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
712
Hello everyone! I have a question regarding the electricity supply and the maximum demand. One energy utility supplies an 18 kVA maximum...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock