any idea why a 12way 3 phase board is buzzing supply cable is 4core 35mm there are no spare ways in db there is a mixture of 32amp rcbo 3 phase breakers lighting circuts etc tightened up all terminations done a load test on l1 l2 and l3 fluxtiuating readings as db supplys photo studio one thing i have noticedc is the db is not balanced very well
 
We had this once when doing a pir turned out to be a central battery emergency lighting system wired up wrong and it backfeeding the board with a dc supply
 
Could be harmonics, are the phases coming through individual holes into a metal DB ? or is the entry slotted.

Are there any lighting relays in the board, they sometimes buzz, the same is there any contactors nearby that would transfer the sound into the board.

Are there any hotspots on the board ?
 
Faulty main switch/breaker?

Turn each rcbo/mcb off one by one and see if the buzzing stops, lastly turn main switch off.
 
Last edited by a moderator:
Lenny could well be the problem will get tong testers on individual circuits when all kit in photo studio is working had a similar problem in there large lighting circuit on 6amp breaker pulling 8.6amps
 
I bet you got dimmers on lighting somewhere???? switch dimmers off see if mcb stops buzzing, on the other hand if no dimmers then probably faulty mcb.
 
if its possible without turning off any sensitive equipment switch each circuit off till the buzzing goes off , then check the load of that circuit ,and the Mcb rating ,also check the connections and make sure they are not loose
 
Couldn't solve problem as can't switch breakers off due to a busy photo studio tightened all connections still buzzing its a dorman smith board a right mess and not possible for me to clamp meter around cables from rcbo as lack of space plus didn't want to cause any tripping of breakers just have to put up with the buzzing for now
 

Reply to buzzing 3 phase board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
10
Views
776
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
878
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Due to an increase in load for a subman, I now need 2 phases for an outbuilding. Original design was 63a supply, but now an electric shower and...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock