Hi. I'm currently doing a 2 day C&G 2377 course.
We've been given some mock exams, their are two question that I am stuck on.
Can anyone help, preferably also with the page in the 4th Edition COP that I can find the answer.
1. Where equipment has a protective conductor current designed to exceed 3.5mA, one requirement is that a label is fixed adjacent to the equipment primary power connection, which includes the wording.....
a. Possibility of high touch current.
b. danger high touch current.
c presence of high touch current.
d. warning: high protective conductor current.
2. Equipment with an earth leakage current designed to exceed 3.5mA shall:
a. have a label permanently fixed indicating the value of the leakage current.
b. have internal protective conductors of not less than 0.5mm2 csa
c. be permanently wired or supplied by a plug and socket to BS 4343 (BS EN 60309-2)
d only used in industrial situations
We've been given some mock exams, their are two question that I am stuck on.
Can anyone help, preferably also with the page in the 4th Edition COP that I can find the answer.
1. Where equipment has a protective conductor current designed to exceed 3.5mA, one requirement is that a label is fixed adjacent to the equipment primary power connection, which includes the wording.....
a. Possibility of high touch current.
b. danger high touch current.
c presence of high touch current.
d. warning: high protective conductor current.
2. Equipment with an earth leakage current designed to exceed 3.5mA shall:
a. have a label permanently fixed indicating the value of the leakage current.
b. have internal protective conductors of not less than 0.5mm2 csa
c. be permanently wired or supplied by a plug and socket to BS 4343 (BS EN 60309-2)
d only used in industrial situations