OK then, long story short; relative has had her old (housing assoc prop) back boiler removed and a new combi installed. The plumbers left the combi's flex temporarily dogged into a plug top and plugged into a socket outlet over the worktop with the assurance that the sparks would be along the next day to make the final connection. I thought I'd show my face when they pitched up and was relieved to find them attempting to pull what I assumed was to be a new circuit through the over-packed mini trunkings and back to the existing C/H mcb in the C/U. I returned at day's end to find all working as per and Carter's aunt more than happy with it.
I then got a late night call from her talling me that all the sockets were tripping out, after running her through a few basic checks it seemed like the Cent Htg breaker was taking no part in proceedings at all???
Next morning confirmed that they hadn't run a seperate circuit at all and their switched FCU was in fact spurred off the washing machine spur which sits on the kitchen ring cct. Carter's sainted aunty then informed me that "...yes they were struggling to get one of their cables through the 'ole, I think they gave up in the end."
hmmmm. that'll explain that then.
So a call to their clerk of works ensued followed by him attending and I quizzed him along the lines of "so why didn't you pull a seperate cicuit? What about cumulative earth leakages? and more importantly if a fault develops with the ring circuit then she'll lose all heating and vice versa?"
A few days later following his consultation with their engineer he came back proffering...
He was referring of course to the illustration at Appendix 15 as justification for the validity of the circuit arrangement. He also offered the fact that...
So gents, where does this practice (of spurring a central heating supply off a ring circuit) sit in relation to sec. 314 Division of Installation? Just can't see how it satisfies the requirements here?
I then got a late night call from her talling me that all the sockets were tripping out, after running her through a few basic checks it seemed like the Cent Htg breaker was taking no part in proceedings at all???
Next morning confirmed that they hadn't run a seperate circuit at all and their switched FCU was in fact spurred off the washing machine spur which sits on the kitchen ring cct. Carter's sainted aunty then informed me that "...yes they were struggling to get one of their cables through the 'ole, I think they gave up in the end."
hmmmm. that'll explain that then.
So a call to their clerk of works ensued followed by him attending and I quizzed him along the lines of "so why didn't you pull a seperate cicuit? What about cumulative earth leakages? and more importantly if a fault develops with the ring circuit then she'll lose all heating and vice versa?"
A few days later following his consultation with their engineer he came back proffering...
"...that circley drawing at the back of that red book you showed me."
He was referring of course to the illustration at Appendix 15 as justification for the validity of the circuit arrangement. He also offered the fact that...
as if this was going to impress or somehow nullify the existence of BS 7671 sec. 314 completely....we've done over 4oo of these so far; all the same way...
So gents, where does this practice (of spurring a central heating supply off a ring circuit) sit in relation to sec. 314 Division of Installation? Just can't see how it satisfies the requirements here?