LEDs all the way now lol, wouldnt fit anything else. Prob what hes gonna end up with.you can wing the 3% for lighting if you fit all LED lights. this could allow a 25mm SWA for > 40A.
Discuss Cable size in the UK Electrical Forum area at ElectriciansForums.net
LEDs all the way now lol, wouldnt fit anything else. Prob what hes gonna end up with.you can wing the 3% for lighting if you fit all LED lights. this could allow a 25mm SWA for > 40A.
If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.Is there any other factors i need to take into consideration for that run of cable?
I must admit this sentence has perplexed me, and I'm probably missing something.If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.
but only if there are extraneous parts in the garage. ?If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.
For 2-core SWA that only happens by time you get to 70mm, expensive!
If smaller SWA (but above 10mm) it can be cheaper to run a 10mm coper CPC in parallel with the SWA.
think he means as a bonding conductor. see post #15.I must admit this sentence has perplexed me, and I'm probably missing something.
If we were talking about the main earthing conductor for the installation at the house I'd get it.
But we are talking about a circuits CPC here aren't we, so doesn't it just have to meet 543.1.3, and be equal to line conductor if less than 16mm sq?
Aha thank you.think he means as a bonding conductor. see post #15.
Its a TT system at the house and will be made TT at the shed, Im not using the armour as a cpc for the shed, only for the sub-main cable which will be protected by a 100ma s-type RCD. I will install a spike at the shed.If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.
For 2-core SWA that only happens by time you get to 70mm, expensive!
If smaller SWA (but above 10mm) it can be cheaper to run a 10mm coper CPC in parallel with the SWA.
The OP described it as "16mx8m metal shed" so I assumed the building itself would be bonded by the supply CPC and is an extraneous conductive part in itself.but only if there are extraneous parts in the garage. ?
Is there any chance the house will become PME (TN-C-S) at any time? If not, then I would use the armour to link both as well as an earth rod. Generally the lower the Ra the better and multiple earths allow less chance of a single point of failure.Its a TT system at the house and will be made TT at the shed, Im not using the armour as a cpc for the shed, only for the sub-main cable which will be protected by a 100ma s-type RCD. I will install a spike at the shed.