U
uksparks
Hi,
Are ceramic hobs prone to problems with RCD's when the hob is a few years old?
I changed a board yesterday, despite a couple of minor problems, when the lady (nearly 90) went to put her dinner on, as soon as she turns any ring on it trips the RCD... I felt bad to be honest.
I am going back later to PAT test the hob and just try disconnecting the other circuits on that RCD to eliminate anything else just encase its a build up of leakage, but did measure the leakage on the other circuits and it was less than 1mA so unlikely to be that.
Everything else is working fine, I did call her late last night to check she was ok and nothing had tripped as was concerned as she was elderly, she said it was all ok, so I can only think its the hob with a fault, unfortunately if it is, its one of those things you don't find out until you switch it all back on.
any ring? bit suspicious, can understand it if just one ring trips could be a more sinister fault elsewhere in the installation, good hunting
could well be a N-E fault. shows up when a load is applied. has even been known to trip the other RCD.
I found it, it was the cable feeding the hob from the outlet to the hob, so the flex, it was a neutral to earth fault, looks like it had been pinched.
Reactions: 1 person
had the pikeys been?
Reactions: 3 people
Ceramic Hob
uksparks,
telectrix,