Hi J, IIUC with an upfront RCD (same position as TT case) the RCD would sense current in L and not N as it's now going back through the rod. And so it'd trip. We would still need a rod (at the PME terminals in your pic) but now we just use it to disconnect the installation rather than put in many rods and try to keep touch voltages down.
 
Last edited:
But it's not fault current, it's any residual installation neutral return current which is able to lift the MET and all exposed conductive parts. The neutral current is surely still balanced in the tails since it's got to be the same as any live current. (There is no earth fault in the installation during this condition to make it otherwise)
 
I can see the logic in it to be honest IET have produced guidance notes on this before but NICEIC inspectors would give you a berating for having 2 different earthing arrangements . So when you are asked for earthing arrangement at origin what would you put down TNCS, TT or will there be a new classification code TNCS/TT?
Would you have to install a rcd on tails from the meter before they enter an AMD 3 board rated at 30mA, or would you be able to install an rcd with upto 1A tripping current as it is for a dribution circuit on a TT system? Could you decide to ignore the TT side of it and continue as for TNCS as the TT part would only come into play when DNO lose neutral on their network. I don’t mind as I am on a trusty old TNS supply at the moment lol.
 

Reply to Changes are coming, what do you all think in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
305
Hi got a 8 panel solar system on bungalow, changing the board to 18th edition spd board Solar feed is chased into wall so will this need a type B...
Replies
4
Views
281
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
761
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
637

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock