Reaction score
1
I need to run new wiring down a cavity block wall.
It is possible for me to chase it but it doesn't seem like a good idea.

What options are available to me?
I loathe surface mount and will do pretty much anything to avoid if.

-Thanks
 
chase it. you are allowed 1/3 of the thickness of the block vertically, and 1/6 of the thickness horizontally. is the wall plastered? if so, that's enough for your cables. cut deeper for socket boxes, but be wary if it's hollow block.
 
A dedicated wall chaser is your friend, here, as you can set the disc depth to the minimum you need and no more, and know it will be stuck to. Hire one with a dust extractor and you're good to go. Use it also to run the lines for your boxes for the same reason and go easy on the hammer afterwards - lots of little light taps will do far better than a big whack which takes the block out!

You might also like to have a bag of readymix mortar or bonding coat to hand - just in case it all goes wrong!
 
It's basically impossible to run a cable unsupported in a cavity wall to current regulations.

I don't think that's what the OP is asking. He's asking about hollow blocks - that's the ones that look like an '8' if you stand them up.
 
Agh my bad. Ignore my comment then. And make sure you don't knock out to much.

My guess is he already has - else why would he know??! :detective:
 
I don't think he's mentioned hollow blocks - only a cavity wall. Could still be solid blocks. Daz
 
If you can get into the cavity you could drop pipes in like I did on a rewire, see pic below. Was a very neat job actually, the pipes only went up two feet in the cavity though, was a fiddle getting them in as they were 50mm.

As cables cannot just be put into the cavity without some form of protection from debris, falling objects, poly insulation etc, pipes was the best way, just popped up my local fish shop and it didnt cost much, ok it was a fiddle getting it in, but its done now and so easy to rod more cables through.

DSC04930.jpg DSC04931.jpg DSC04954.jpg DSC04955.jpgDSC04964.jpg DSC04969.jpg DSC04926.jpg
 
Whats this piddly thingy label I see at the bottom for ......

01 image.jpg

I reckon that would have been a b*tch of a job to get those pipes in but the end result does you full credit for a real professional finish! Get your label changed to "master craftsman working"!
 
Master craftsman... I don't feel that good yet, but I know I always do a good job, it probably took me an hour to get 5 pipes in, the cavity was only 60mm I think and the pipe was 50mm, that's why I had to knock a few bricks out to get it in as there were a couple of ties in the way! But yes, this was a job I was pleased with.
 
If you can get into the cavity you could drop pipes in like I did on a rewire, see pic below. Was a very neat job actually, the pipes only went up two feet in the cavity though, was a fiddle getting them in as they were 50mm.

As cables cannot just be put into the cavity without some form of protection from debris, falling objects, poly insulation etc, pipes was the best way, just popped up my local fish shop and it didnt cost much, ok it was a fiddle getting it in, but its done now and so easy to rod more cables through.

View attachment 20876 View attachment 20877 View attachment 20878 View attachment 20879View attachment 20880 View attachment 20881 View attachment 20882

Looks like those compression glands are for supply tails , and db looks metal clad wot I'm getting at is metal ( ferrous ) enclosure just wondering if you have slotted knockouts or have tackled that in anyway? . Must say like the job very tidy will be making a mental note of you tekkers there .
 
I have understood that its a no no with wiring in cavity's unless mechanical protection blah di blah and don't really get why ( just becouse cable is not supported ?? ) my best guess . But I guess that cables in a 9 meter vertical galv trunking is supporting cables???

Just came into my head maybe cavity wiring may bring on the occurrence of damp issues ?? Just a though
 
Yes both boards are metal, the one at the top, the compression glands, I drilled these in ready to put the supply cables in as you pointed out and the little black one was to put the earth in. There are knockouts on the bottom board, I used them for trunking to the garage stuff etc and fire alarm switch.

Where I carefully cut out the top board to take the cables in the back instead of through the top in a header thing, I have superglued a rubber edge (got loads of it from eBay for next to nothing) on as per the photo below to ensure no damage can be done to the cables over the cut edge. I didn't do that on the bottom as the edge was very smooth and rounded over so didn't feel it needed it to be honest.

I am sure you can see I take care in my work and try to think of the what if's and buts.

DSC04966.jpg DSC04968.jpg
 
I'm was purely commenting on those stuffing glands as all live and neutral conductors should enter a ferrous enclosure via the same hole as to prevent eddy currents on you're earthed metal/ferrous enclosure ( db ) but a way around that is to cut a slot between each hole so I'm tolled , yes I agree you do a tidy job and obviously have pride in wot you do good job
 
I agree about the eddy currents, but to be honest, its only drawing 90A I think on the three phase board, about 30A per phase, it's not something I'm going to loose sleep over, yeah if it was significantly more then I would have put them in the same hole. The 24 hour board, they did enter through the hole on the right in one, it was only the top one that was like it. I appreciate eddy currents are obviously not made up, but at what current would you expect to experience them, or anything noticeable?

- - - Updated - - -

I'm going now else Ill be late...
 
When I first read the original post, I assumed it was a 2 skin cavity wall he was referring to, ie. two breeze-block leaves. You're probably right though with the hollow blocks, it's just that I've never heard of them referred to as 'cavity blocks'. Daz
 
I don't think there are exceptions to the regs just best we abide regardless if we think!( as u or I don't know exactly!! the risk is with eddy's ) the risk is minimal , things to take into account is maybe wot if the installation purpose changes and that board starts using more than 90a ?? The installation obviously requires more than the usual property as it was deem'd to req three phase and least two additional db's , I'm not trying to drag into a debate was just a pointer , issues concerning eddy current's I can only guess so I won't as il probably get leathered on this site!
 

Reply to Chasing cavity block wall in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
528
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
200
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
I have a large gym in the garden and it gets ridiculously hot in the summer. I have utilised pretty much every inch of space and do not want to...
Replies
23
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock