I Have a chiller to feed power to and i'm having a play with the calcs prior to the designer.
The cable run is 60m directly clipped
I'm arriving @ 16mm CSA cable but i'm cncerned about the max start up.
Also thinking 50A C type or maybe 63A C type - but it mentions REC 80A
Electricial Data
Nominal Run Amps (A) 47.20
Maximum Start Amps (A) 202.30
Control Circuit (VAC) 24VAC
Mains Supply (V) 400/3/50
Permanent Supply (V) 230/1/50
Rec Mains Fuse (A) 80.00
Rec. Permanent Fuse (A) 4.00
Max Incoming ) Mains (mm²) 35.00
Cable Size ) Perm (mm²) 2.50
Compressor
Motor Rating (kW) 11.60
Nominal Run Amps (A) 19.80
Locked Rotor Amps (A) 175.00
Crankcase Heater Rating (W) 50.00
Type of Start Direct On Line
Condenser Fan
Motor Rating (kW) 0.60
Full Load Amps (A) 2.62
Whats the thoughts of you guys?
Ta
I Have a chiller to feed power to and i'm having a play with the calcs prior to the designer.
The cable run is 60m directly clipped
I'm arriving @ 16mm CSA cable but i'm cncerned about the max start up.
Also thinking 50A C type or maybe 63A C type - but it mentions REC 80A
Electricial Data
Nominal Run Amps (A) 47.20
Maximum Start Amps (A) 202.30
Control Circuit (VAC) 24VAC
Mains Supply (V) 400/3/50
Permanent Supply (V) 230/1/50
Rec Mains Fuse (A) 80.00
Rec. Permanent Fuse (A) 4.00
Max Incoming ) Mains (mm²) 35.00
Cable Size ) Perm (mm²) 2.50
Compressor
Motor Rating (kW) 11.60
Nominal Run Amps (A) 19.80
Locked Rotor Amps (A) 175.00
Crankcase Heater Rating (W) 50.00
Type of Start Direct On Line
Condenser Fan
Motor Rating (kW) 0.60
Full Load Amps (A) 2.62
Whats the thoughts of you guys?
Ta