Hi guys,

When performing an earth continuity test on class 1 appliances can you get away with just using a 200mA current on every piece of equipment?
Having been on the 2377 course they say to use 1.5 times the fuse rating upto 26A for non IT.
Need clarification as to what is right. :confused5:

Cheers
Scarlet
 
a current of a few mA may not find as poor connection on a kettle, say, but a fault current could blow it away, leaving the metal casing live. that's why we use 20A.
 
As Tel said....if the earth is hanging on by one strand 200ma will show a good reading......pump 26a through it and it wont,it just proves the connection should be up to a fault current.
 
The problem with most modern hand held PATs are that the earth bond test only provides 100mA. The older 230V PATs apply the full 20 - 26A, dependent up model/make.

This is likely to be Ok where there's a possibility that damage might be done to sensitive electronic equipment, although I often wonder what damage might happen (filtering circuits exempt) when the tester should test only the exposed conductive part back to the earth pin on the plug.

You can still pick up a second hand Robin 5000 series PAT for less than £350.
 
Hi guys,

When performing an earth continuity test on class 1 appliances can you get away with just using a 200mA current on every piece of equipment?
Having been on the 2377 course they say to use 1.5 times the fuse rating upto 26A for non IT.
Need clarification as to what is right. :confused5:

Cheers
Scarlet

I wonder what the Code of Practice states? ......................


Have you read it? -and, if so, what do you suggest?
 

Reply to Class 1 Earth Continuity for PAT test. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am a new PAT tester for a school, and I am stuck testing a plasma globe. It has a two core wire going to it, but no class 2 mark on the...
Replies
18
Views
2K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
659
Hi All I’ve come across this heater Ariston Andris Lux Undersink Water Heater 2kW 10Ltr - Screwfix -...
Replies
14
Views
2K
Sorry if this thread is in the wrong section, I was always led to believe that a TV was class 1 for PAT testing, however the TV has a metal earth...
Replies
8
Views
1K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
585

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock