Replacing lights in office , where there is no earth continuity on the existing circuit.
The new lights are Class II & require no earth.
The client refused rewire of the area, the cabling is T&E but no earth connection..is this legally correct.
 
When you say no connection does this mean there are cpcs but there is no continuity through them.
 
  • Like
Reactions: timhoward
This analogy may help: even if you are plugging class 2 appliances into a radial sockets circuit the circuit still requires a cpc to protect the cables.
Same for lighting circuits - even if the cpc isn’t connected to each luminaire it needs to be connected to the next length of cable and so on.
 
A 'short' 2 core flex via a connector may be permitted for the light, but the circuit wiring should incorporate a cpc as stated by others.
 
  • Agree
Reactions: Petej999
This analogy may help: even if you are plugging class 2 appliances into a radial sockets circuit the circuit still requires a cpc to protect the cables.
Same for lighting circuits - even if the cpc isn’t connected to each luminaire it needs to be connected to the next length of cable and so on.
Totally agree… it would be easier to install new circuit to the area.
 
Is it grid ceiling? Can you get a Zs at any of them? I tend to find the one that works and start there using quickwire flex connectors
 
It’s a complete mess… those above have insisted on fitting these lights without even the thought of finding the fault..
 
Has anyone made an attempt to resolve it. Are the light switches earthed.
 
So has anyone tried to resolve it.
 
  • Like
Reactions: DPG
Their remit was fit Class II fittings
 
as above.you fix the broken cpc issue before doing any specified works or walk.
 
  • Agree
Reactions: loz2754
What will you put on the certification for earth continuity.
 
  • Like
Reactions: DPG and loz2754
  • Agree
Reactions: westward10
What will you put on the certification for earth continuity.
It’s not my job I've only questioned the sparks involved …I won’t be signing anything
 
This analogy may help: even if you are plugging class 2 appliances into a radial sockets circuit the circuit still requires a cpc to protect the cables.
Same for lighting circuits - even if the cpc isn’t connected to each luminaire it needs to be connected to the next length of cable and so on.
Other than when it forms an earthed sheath around the live conductors, how does a CPC protect a cable?
 
Other than when it forms an earthed sheath around the live conductors, how does a CPC protect a cable?
I accept I didn't word it well, but my meaning was it provides a reliable return current path for edge cases when strange things have happened upstream.

The (obscure) old example coming to mind was when a fuse was removed for the lighting circuit (by customer), the lighting circuit cable was cut, and BANG the main fuse blows. It turned out the CU was wired reverse polarity. If that circuit hadn't had a cpc the customer may have found out about the reversed polarity a much nastier way. Granted, that one is not going to happen every day.
 
  • Like
Reactions: Pretty Mouth
So what is the reason for a cpc in final circuit that is supplying a class 2 fitting in a commercial environment.Is this a regulation requirement. I agree it's required in a domestic environment as a class 2 light could be easily changed with a class 1 fitting by the home owner .
 
it's there so hopefully a nail or screw penetrating the cable will short L-E and thus result in the OCPD tripping out and killing the circuit. ( apart from a L-E short at a classI fitting).
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Class II
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
cliffed,
Last reply from
telectrix,
Replies
22
Views
2,172

Advert