Replacing lights in office , where there is no earth continuity on the existing circuit.
The new lights are Class II & require no earth.
The client refused rewire of the area, the cabling is T&E but no earth connection..is this legally correct.
 
This analogy may help: even if you are plugging class 2 appliances into a radial sockets circuit the circuit still requires a cpc to protect the cables.
Same for lighting circuits - even if the cpc isn’t connected to each luminaire it needs to be connected to the next length of cable and so on.
 
A 'short' 2 core flex via a connector may be permitted for the light, but the circuit wiring should incorporate a cpc as stated by others.
 
This analogy may help: even if you are plugging class 2 appliances into a radial sockets circuit the circuit still requires a cpc to protect the cables.
Same for lighting circuits - even if the cpc isn’t connected to each luminaire it needs to be connected to the next length of cable and so on.
Totally agree… it would be easier to install new circuit to the area.
 
Is it grid ceiling? Can you get a Zs at any of them? I tend to find the one that works and start there using quickwire flex connectors
 
as above.you fix the broken cpc issue before doing any specified works or walk.
 
This analogy may help: even if you are plugging class 2 appliances into a radial sockets circuit the circuit still requires a cpc to protect the cables.
Same for lighting circuits - even if the cpc isn’t connected to each luminaire it needs to be connected to the next length of cable and so on.
Other than when it forms an earthed sheath around the live conductors, how does a CPC protect a cable?
 

Reply to Class II in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
533
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock