On a test & inspection today, I came across an older Wylex split load board that had been modified to add RCD protection for all circuits (see photo). The main switch was replaced with an RCD (despite there being room to add the second RCD to the left of the main switch). So a fault (or RCD test) on the LH bank of circuits trips both RCDs.

I'm inclined to code this as C3, since it defeats the object of trying to provide some discrimination, not necessarily potentially dangerous.

I'm wondering if others would be thinking this is an unapproved modification of a board, and perhaps should be a C2?

The EICR will be unsatisfactory anyway, there are other issues like holes in the front cover, an RFC with open circuit rN, some unearthed metal fittings, etc.
 

Attachments

  • Series rCDs.jpg
    Series rCDs.jpg
    396.5 KB · Views: 46
Not potentially dangerous but certainly annoying, new main switch is about £3, a couple of jumpers and you have a dual board. ?
 
  • Like
Reactions: SJD
C3 IMO.
 
  • Like
Reactions: SJD
I would agree with c3
 
  • Like
Reactions: SJD
This is one instance where I disagree with BPG 4.

The only reference similar to a main switch RCD is this, under the heading "do not require reporting":

Installation not divided into an
adequate number of circuits to minimise
inconvenience for safe operation, fault
clearance, inspection and testing

In my opinion this would be C3, due to possible danger of falling downstairs in the dark etc.
 
  • Like
Reactions: SJD
Thanks for the replies.

The point from Ioz2754 about being an item noted as not requiring reporting, I'd assume this refers to something that was compliant at the time of installation. I'd like to think modifying a board to put two RCDs in series was not a compliant thing to do at the time it was done.
 
  • Like
Reactions: loz2754
Thanks for the replies.

The point from Ioz2754 about being an item noted as not requiring reporting, I'd assume this refers to something that was compliant at the time of installation. I'd like to think modifying a board to put two RCDs in series was not a compliant thing to do at the time it was done.
Indeed. I would agree with this. Why anyone would think this was a good idea....
 
  • Agree
Reactions: SJD

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

SJD

Mentor
Arms
~
Joined
Location
Braccan heal
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
Running own small electrical company.

Thread Information

Title
Code for main switch replaced with RCD
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
SJD,
Last reply from
loz2754,
Replies
6
Views
8,296

Advert