Hello guys

I need to install X4 95mm tri rated tails in some metal Kopex
Nominal Overall Diameter18.7mm

What size kopex would suit this cable bunch and does anyone have current carrying capacity guides as for a 200a supply 70mm tri seems capable in some cases but 95mm might be needed when bunched in conduit
 
Assuming it is TPN arrangement then I would guess the CCC is not much different from 4-core SWA in duct, so 70mm is enough for 200A.

But that is also the value for XPLE rated at 90C so you would need to take care that the end terminations are rated for the sort of temperature the cable will run at.

No idea about the Kopex, only ever seen it for sale in 20/25mm sizes and that ain't taking 4 * 70mm!
 

Reply to Conduit Calc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
421
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
917
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
It seems to be easy, these days, to buy fittings (often containing resin) that allow someone to tee into a pre-existing SWA cable. Some of these...
Replies
6
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock