Discuss confused.. in the UK Electrical Forum area at ElectriciansForums.net

T

terry198920

I am only a trainee ( so don't bite too much) a friend of mine called out british gas to fix his boiler.. Whilst he was there he checked the electrics.. Said the earth loop was greater than 200 ohms on the ring main and they should get a spark out asap.. So he asked could i pop down and and have a look before they call in a spark ( to see if i could see what the issue was ) it is a TT supply as far as i can tell with a wylex board rewireable fuses with separate RCD installed.. Tested the board.. 0.28ohms..PFC was 0.956kA.. Tested the rcd at 1/2.. X1 and x5.. All within limits.. Tested the socket where the PLUMBER checked and here is where i get lost.. Earth fault loop impedance Test with a megger1730.. 1st test setting was L-L 0.60.. L-N was 0.60 and the setting l-pe was 800ohms.. Is the setting L-PE the important reading yes? And whats the outcome..
 
hang on. go back to basics. start with a Ze. on a TT,
 
What do you mean by zs at the board? with main earth disconnected and test between live neutral earth? I always assumed ze was at origin.. Zs furthest point on a lighting point ect..
 
Last edited by a moderator:
What do you mean by zs at the board? with main earth disconnected and test between live neutral earth? I always assumed ze was at origin.. Zs furthest point on a lighting point ect..
 
Forget the earthing arrangements for a moment, if you carry out a Ze at a board and get 0.28ohms and then a Zs on a circuit fed by that board and get 800ohms then the problem is with that circuit isn't it.

All that being said, double check your readings at the board, I find it very unlikely that you will have an Ra (Ze) of 0.28ohms on a domestic TT system unless there are a good few earth rods installed or it is linked to steel reinforcement within the foundations.
 
Skelton.. They have recently had a new incoming supply fitted.. The reason i said tt system is because an earth is running outside to a rod.. My first thought was tns if that helps.. I should of took a picture would explain more as to why i got confused.. Im aware the fault is at the socket.. But is it as simple as finding a loose connection and tighten the earths up..
 
Forget the earthing arrangements for a moment, if you carry out a Ze at a board and get 0.28ohms and then a Zs on a circuit fed by that board and get 800ohms then the problem is with that circuit isn't it.

All that being said, double check your readings at the board, I find it very unlikely that you will have an Ra (Ze) of 0.28ohms on a domestic TT system unless there are a good few earth rods installed or it is linked to steel reinforcement within the foundations.

i don't think he was disconnecting the main earth during test, i reckon thats because of parallel paths that reading was that good.


think about it.


2.5mm--------7.50 milli ohms per metre or 0.00750 ohms OSG 7.41
 
i don't think he was disconnecting the main earth during test, i reckon thats because of parallel paths that reading was that good.


think about it.


2.5mm--------7.50 milli ohms per metre or 0.00750 ohms OSG 7.41

I was coming from the angle of a loose connection on the socket circuit. I also advised re-doing his Ze as I suspect he wasn't doing it properly.
 
I have seen earth rods installed on TNS and TNCS systems. It can be confusing if you are not completly sure of what you are looking for. As has been said 0.28 is VERY low for a domestic TT system unless there a parallel paths e.g. shared metal water pipe with TNCS system bonded next door.
 
Confucius he say.......''don't listen to everyone at once, you'll git mixed up, go around in circles and disappear up your own backside''.
Sort out, for definite, whether it's tt, tns or tncs and then you might get somewhere with your question.
 
this is TT.

220px-Isle_of_Man_TT_Races_RC30.jpg
 
Confucius he say.......''don't listen to everyone at once, you'll git mixed up, go around in circles and disappear up your own backside''.
Sort out, for definite, whether it's tt, tns or tncs and then you might get somewhere with your question.
I don't know what he's on about but it certainly is not Chinese!!
 
No just little old me and 3 x 5/8 rods. Drove 1 in and got about 100 ohms, knocked the second one in and got 20 ish them I thought how low can you go
 
Any idea why they would even be checking the electrics in the first place? After coming out to fix a leaky boiler.
Because the people who come out have sales targets to meet. They semi train them on elctrics and set them loose on an unsuspecting public, as a result little old ladies are coerced into replacing their 16th edition CUs for 17th ones because they've been CONDEMNED! because they're not safe.
Crooks.
I have that on good authority because I have a mate who is a pipe monkey who works for them.
 
Skelton.. They have recently had a new incoming supply fitted.. The reason i said tt system is because an earth is running outside to a rod.. My first thought was tns if that helps.. I should of took a picture would explain more as to why i got confused.. Im aware the fault is at the socket.. But is it as simple as finding a loose connection and tighten the earths up..
so...any evidence of a TN earthing then?
 
Because the people who come out have sales targets to meet. They semi train them on elctrics and set them loose on an unsuspecting public, as a result little old ladies are coerced into replacing their 16th edition CUs for 17th ones because they've been CONDEMNED! because they're not safe.
Crooks.
I have that on good authority because I have a mate who is a pipe monkey who works for them.

I'll second that!

My best pal is a British Gas engineer (he is actually a qualified engineer), and just the other week was called into a disciplinary hearing because he turned up to a job that didn't need doing and the customer had been sold a service that they didn't need. He ended up only carrying out the work that did need doing after making the customer aware of the situation and saving the customer thousands which they were happy about. When he reported back to his line manager about the initial misselling he was torn apart!

Proper scam organisation! They were on Watchdog not too long ago about all this.
 
I'll second that!

My best pal is a British Gas engineer (he is actually a qualified engineer), and just the other week was called into a disciplinary hearing because he turned up to a job that didn't need doing and the customer had been sold a service that they didn't need. He ended up only carrying out the work that did need doing after making the customer aware of the situation and saving the customer thousands which they were happy about. When he reported back to his line manager about the initial misselling he was torn apart!

Proper scam organisation! They were on Watchdog not too long ago about all this.
well...alls i can say is its high time something was done about them...

you dont carry out `works` that dont need doing...its incompetant, slovenly and could be a case for mis-selling.

in fact the police have a term for it:

its called obtaining money/services by deception...
 

Reply to confused.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I saw a Fluke 1653B on Gumtree local to me being sold as faulty. Fault was stated as no continuity between 'N' and 'PE' ports on the resistance...
Replies
3
Views
512
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
512
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top