i was filling in an EICR for a mate and had left my on site guide and reg book at home so i decided to check the net for max zs values for 60898 type b mcbs 6a. 16a, 32a, and 40a but the figures didnt match up with the ones in the reg book. so question what sites do the lads recommend as i was dong it on a mobile device so ended up giving in and waiting till i got hame

thanks
mad spark
 
Most guides (and that includes the OSG and the Internet) may have a "rule of thumb" percentage of 80% calculated on the 'regs' table Zs values.
That may account for the difference.

Also the Zs figures recently have changed in the Bible, but the Internet will rely on people like you and me to keep it up to date. And I CBA!
 
i think keep a photocopy of max zs tables in folder with the certs (have to fill in by hand as dont want to pay for software )
 
  • Useful
Reactions: 1 person
Got them in my head.
 
  • Like
Reactions: Wilko
Hiya lads a stupid query (maybe )
i was filling in an EICR for a mate and had left my on site guide and reg book at home so i decided to check the net for max zs values for 60898 type b mcbs 6a. 16a, 32a, and 40a but the figures didnt match up with the ones in the reg book. so question what sites do the lads recommend as i was dong it on a mobile device so ended up giving in and waiting till i got hame

thanks
mad spark
Easy way to work out type b mcbs is 218.5 volts divided by 5x their rated current
10x for type c
20x type D
Saves you needing to look it up if you've forgotten your books
Fuses ...... not so easy with out a reference to hand
 
For mcbs just memorise a few. For example if you know a 10A you can easily work out a 20A, 40A by just doubling the 10A value. Must admit I knew nearly all of them off by heart until the values changed and my brain now struggles to adapt:)
 
  • Agree
Reactions: 1 person
Easy way to work out type b mcbs is 218.5 volts divided by 5x their rated current
10x for type c
20x type D
Saves you needing to look it up if you've forgotten your books
Fuses ...... not so easy with out a reference to hand
Where did you get that gem from?
Didn't I say that you were a clue'd up spark!
 
  • Like
Reactions: Ian1981
230v x cmin 0.95= 218.5v
32 type b x5 is 160amps
218.5/160= 1.37 ohms.
230v x cmin 0.95= 218.5v
32 type b x5 is 160amps
218.5/160= 1.37 ohms
Lovely - data inputted - thanks a lot. Sometimes when you look at the mathematics of stuff it's like poetry.
Yeah it's just the basics ohms law v/IR
Think the old bs 3871 where
Type 2 x 7rated current
Type 3 x10 rated current
 
and these calcs. go out the window when voltage is more like 240V, and generally, cables will never be operating at their max. temp. of 70 deg. :mad:
 
  • Agree
Reactions: David M and Pete999
and these calcs. go out the window when voltage is more like 240V, and generally, cables will never be operating at their max. temp. of 70 deg. :mad:
This is true however the max values are based on a worst case scenario as bs 7671 tends to er on the safe side of things.
 
  • Like
Reactions: David M

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
fife
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
confusing figures between net and regbook
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
12

Thread Tags

Advert

Thread statistics

Created
martin mcguinness,
Last reply from
Ian1981,
Replies
12
Views
2,183

Advert