I need to run an out door supply.
However the dist board is boxed in.
There is access back entry but that doesn't help glanding a swa.
Could you gland outside to a through box them carry the same cable to the breaker?
Taking an earth leas from the conduit box also.
 
You could do, but it would be better to use a suitably IP rated adaptable box and don't forget to use an outdoor rated gland assembly.
 
I need to run an out door supply.
However the dist board is boxed in.
There is access back entry but that doesn't help glanding a swa.
Could you gland outside to a through box them carry the same cable to the breaker?
Taking an earth leas from the conduit box also.

Yes you can.
 
Well the conduit box will be behind some boxing in and under a lean to

I would leave the box accessible. Not behind some boxing in.
Also the cable from the box to the breaker will have to be RCD protected, depending on installation method.
 
Yes outside the house just behind the cu but inside some boxing in.
All other cables are in the walls from cu
 
  • Informative
Reactions: 1 person
I was going to put it on a 32 amp rcbo
As it's going to an outdoor isolator for a hot tub.
 
I was going to put it on a 32 amp rcbo
As it's going to an outdoor isolator for a hot tub.
What size cable do you intend to run, how far is the hot tub from the C/U, what loading is the hot tub, what installation method are you intending to use.?
 
Hot tub Is 13 amp. Cable run 10m
Planned to use 2.5 swa.
Clipped direct through a garage at high level.
 
I need to run an out door supply.
However the dist board is boxed in.
There is access back entry but that doesn't help glanding a swa.
Could you gland outside to a through box them carry the same cable to the breaker?
Taking an earth leas from the conduit box also.
why do some people think we can do a job for them while on this forum .
take picture of the work it will tell a story.
 
Not to be rude but how is a picture of a wall where I intend to mount a conduit box going to help ?
I'm not at the job right now.
Just wanted to confirm I can gland somewhere else other than at the ccu since its not something I've done ever.
 
This forum always starts off helpful then soon turns to negativity and do you want me to do the job for you.
So helpful, probably get more help on a fitters forum.
take no noticeof buzzlightyear. (nobody else does :)). your plan saounds OK. gland SWA into a adaptable box, carry the tails into the CU ( in pvc tube is a good idea ), add an earth tail for earthing the armour, job's sound.
 
we all need help for time to time. but when you plan a job or start you have to become a engineer has well has a spark .put a plan on a plain paper let the dog see the rabbit .
to help you
 
we all need help for time to time. but when you plan a job or start you have to become a engineer has well has a spark .put a plan on a plain paper let the dog see the rabbit .
to help you.
 
Double post by Buzz. Name and shame until Dan sorts it out! Careful out there - it could be you next!
not again.
 
  • Funny
Reactions: Rpa07

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Connection issue with swa
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
44

Advert

Thread statistics

Created
Leejohnson222,
Last reply from
Ian1981,
Replies
44
Views
3,717

Advert