kes123

Hi all I am new to this and practising using a Megger 1553 tester. I Isolate the system connect the line to earth and my meter starts to test and then its like the circuit gets broken after a split second and no reading can be taken.
I have conected a long lead from the earth at consumer unit to the earth at the light fitting I am checking and it reads continuity. But method 1 just won't seem to work.

Any ideas

cheers
 
Long lead method.
Connect lead at earth terminal in CU, and connect other end through your tester to any given earth terminal in the circuit, the highest reading you get is the R2 value for that circuit.
R1+R2 method.
Join Line to CPC in CU, take reading at any point on the circuit between L-CPC the highest value you get is the R1+R2 for the circuit. On a lighting circuit make sure the switch is ON or you will not get a reading at the lamp holder.

If your machine is going off after a few seconds then check the batteries, if all is well you are doing something wrong.

Cheers........Howard
 
we all make mistakes, as the hedgehog said, climbing off the bog brush.
 

Reply to Continuity resistance tsting problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
734
Chaps - having problems with a new Megger MIT420/2 insulation/continuity tester 'oscillating' and failing to give stable resistance readings in...
Replies
2
Views
635
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock