Hello. The variable speed switch on our old jacuzzi recently broke. The 120V 11.5amp 50/60hz motor is still functional but parts are no longer available. I tied the switch wires (see pic) and was able to control the speed using a 120v 60hz household dimmer placed directly on the line feeding the pump but am curious about the durability/safety of this choice or if there's a better option. We're replacing the tub next year.


Thanks.
 

Attachments

  • pump dimmer.jpg
    pump dimmer.jpg
    159.7 KB · Views: 4
  • Tied switch wires.jpg
    Tied switch wires.jpg
    63.2 KB · Views: 3
Last edited by a moderator:
Assuming the dimmer is this one :
I don't think it's up to the job.
It's rated at 600W for a resistive load, which equates to 5A at 120V.
You have I think a bit of an inductive load, which as you point out can be up to 11.5A, more than double the rating of the dimmer.
If you want to do this, I would suggest you seek a controller designed for that load, but hacking a circuit on a hot tub with non-original parts is a big safety responsibility, and I would not do it if other perople were going to use the tub!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Controlling 120v VS pump with a dimmer switch
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
andrewpasetti,
Last reply from
Avo Mk8,
Replies
1
Views
956

Advert