In my flat the main earth is the cable pictured below it has 7 strands any idea what size this is?
And if it would need to be upgraded for a cu change
The bonding is in 6mm but is easy to change to 10mm but I guess that's irelavent if the earth is 6mm?
The conduit system the 16mm tails come up in with the main earth gives a better ze than the main earth cable 0.15 ohm on
conduit
60 amp fuse in rifled board
And if it would need to be upgraded for a cu change
The bonding is in 6mm but is easy to change to 10mm but I guess that's irelavent if the earth is 6mm?
The conduit system the 16mm tails come up in with the main earth gives a better ze than the main earth cable 0.15 ohm on
60 amp fuse in rifled board