Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for live, 2 for neutral & 1 fir the CPC. No earth tag at either end of the SWA so can assume it's not being used as a CPC. Should I put this down as a departure or C3.
 
Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for live, 2 for neutral & 1 fir the CPC. No earth tag at either end of the SWA so can assume it's not being used as a CPC. Should I put this down as a departure or C3.
The armour should be Earthed. But for the lack of ring continuity on the cpc then I would suggest that this needs to be rectified.
 
If a core is being used as the CPC, and they earth the armour, what is the departure?
 
If they earth the SWA correctly either end while I'm here wouldn't it just go down as a departure?

No, you don't record departures on an EICR, that is something that you record on an installation certificate.

An EICR is only concerned with reporting on the suitability for continued use of the installation by recording non-compliances which have a safety implication or that could be changed to improve the safety of the installation.

A ring circuit is required to have a CPC in the form of a ring unless it is formed by a metal covering or enclosure containing all of the conductors of the ring (543.2.9)
So as it is now I'd be inclined towards C3 but if the armour is properly connected at each end (and 543.2.7 has also been complied with) then no code.
 

Reply to Departure from BS7671 or C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
742
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock