Discuss Designing with diversity on sockets in the UK Electrical Forum area at ElectriciansForums.net
Invest in a clamp meter. When you go to properties just check what load is being used by clamping the line meter tail. After a few jobs you'll start to build a mental picture of what a domestic property actually uses.
Common sense should prevail to avoid compromising the optimum division of an installation, solely to satisfy a diversity calculation.
Not sure you quite understood what my post was asking, it was to do with the wording of the OSG, not to do with the installation of the wiring. The maximum demand box on the Electrical installation certificate (filled out after the install) seems to have various ways in which it is calculated.
Am I right in saying that that quick guide says you need to be concerned about overloading a CU with a mains switch that is rated at 100A.
And the answer is to put the additional load onto a sub board.
Calculating load is witchcraft.
I'm doing and EICR on a 1990 instal that hasn't been touched in thirty years, no additions and no periodicals.
There are the following,
32A shower (7kw) =30.5A
32A hob (6kw) and socket = 31A
32A kitchen sockets = 32A
32A lounge Sockets = 12.8A
32A up sockets =12.8A
32A up sockets = 12.8A
20A oven(3kw) and socket 18A
16A immersion (3kw) 13A
8 x 6A lights total (15kw) 7.2A
Now this comes out to around 200A.
In two CUs but the second is off the output of the firsts main switch.
Oh and there is a 60A switch fuse, off the source, for a granny Annex I've not even looked at yet.
Main fuse is original, so never blown.
Tempted to turn it all on and clamp it if the main fuse lasts long enough for me to reach the incomer.
What makes you think the main fuse won't last?
Now, I could probably knock 25A off the sockets and 3 or 4 off the lights but I cannot see for the life of me how this was ever signed off.
In general the standard of the install is quite good.
Has it been signed off or not?
Reply to Designing with diversity on sockets in the UK Electrical Forum area at ElectriciansForums.net
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...