I just got some new certs. Asks for disconnection times in circuit info
can someone tell me where 5s disconnection applies under the 17th edition
as it does not seem to be just hard wiring or sockets anymore (Big red is making me Dizzy)
 
In a TN 230V system, maximum disconnection time for final circuits up to 32A is 0.4 seconds. Final circuits exceeding 32A are permitted up to 5 seconds. BS7671 411.3.2
 
In a TN 230V system, maximum disconnection time for final circuits up to 32A is 0.4 seconds. Final circuits exceeding 32A are permitted up to 5 seconds. BS7671 411.3.2

Dont forget distribution circuits e.g. main CU to garage CU, this sub main is also permitted 5sec
 
TT system 0.2 seconds
 
I think the proective device must be greater than 32 amp to allow 5 secs rather than 0.4. Most cooker circuits are 40 or 45 amp so 5 secs is allowed.

Page 282 of the regs indicates that if the cable was 4mm then depending on the ref. method the CB would be unlikely to be greater than 32 amps therefore min. cable size must be 6 or 10mm.
 
I thought if a cooker switch incorporates a socket outlet then the disconnection time is ALWAYS 0.4 sec regardless of the size of the MCB but I can't find it in the regs.
 
I thought if a cooker switch incorporates a socket outlet then the disconnection time is ALWAYS 0.4 sec regardless of the size of the MCB but I can't find it in the regs.

Your bang on mate. But he said without a socket outlet it can be 5 seconds disconnection time. But if its only 32A then its still 0.4seconds.

Cheers
 
Disconnection Times


230v final circuits in a TN system not rated greater than 32A must disconnect within 0.4 seconds under fault conditions. 411.3.2.2
230v final circuits in a TT system not rated greater than 32A must disconnect within 0.2 seconds under fault conditions. If disconnection is made by a fuse or mcb and all extraneous conductive parts are connected to the main equipotential bonding then a disconnection time of 0.4 seconds is permitted. 411.3.2.2
Under fault conditions in a TN system, circuits over 32A including distribution circuits must disconnect within 5 seconds. 411.3.2.3 Under fault conditions in a TT system, circuits over 32A including distribution circuits must disconnect within 1 second. 411.3.2.
All this can be found in the sticky Brightspark posted.
BS7671 : Reference
 
Last edited by a moderator:
Table 41.1 in 17th Ed book refers to this.

I have been told that if a final cct is off a sub-main board then the disconnection time is 5 sec. Is this true? I cannot find any reference to this.
 
no mate only if its a distribution circuit 5 secs for tn and 1 sec for tt
final circuits are 0.4 for 32a and under and 5secs for over 32a in tn systems
and final in tt are 0.2secs under 32a and are 1 sec for over 32a in tt sytems like mac said
this is what we was taught in 2391
 

Reply to Diconnection times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K
Hello all Well, been putting it off, but I need to upgrade my 17th edition to the 18th. Not been a practising sparky for over 5 years, but I have...
Replies
19
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Does anyone else get emails and phone calls from companies and agencies say we seen your CV and we want you to apply for our job. And when you...
Replies
4
Views
651
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
277

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock