- Reaction score
- 157
You are correct if there are no wiring problems. For filter caps (etc) it should be a max of less than 1 mA/device (cookers and IT equipment can be a few mA). So nowhere near the 120 mA apparently missing.If it's a TT system then the current returning via earth should be almost zero as there should be no connection between earth and the live conductors (other than filtering caps etc that can cause a small leakage.)
However, even a TT supply Neutral is connected to Earth at the distribution transformer. If there is a short or low resistance connection between the house Neutral and the local ground Earth, then stray current can flow (immersion heaters are prone to cause this type of N-E fault). If his clamp-meter readings are correct, then I would take a bet that the "lost" current was probably going via the Earth connection. Should be easy enough to determine using a suitably sensitive and accurate clamp meter.
Another thought is... 'an old 50mA RCD'?? Is that what the protective device is? Or is it an old 50 volt voltage-tripping ELCB that sits between the Earth spike and the CU Earth busbar? That would explain why the '50 mA RCD' is not tripping. That was what used to be fitted in ages past. I have seen plenty in old houses in rural locations.
Another concerning thought - Earth is to an old lead water pipe - only house on the Estate like that now... are you sure - do all the other houses have proper Earth Rods or were they upgraded to supplied PME Earths by the network company sometime in the past? Your water pipe should be formally tested.
Although 120 mA is not a large stray current, it does represent about 30 watts of power - so the cause really should be tracked down and remedial action taken.
So, sorry, it sounds as if you should get a full EICR test carried out.