has anyone ever been in contact with manufacturers regarding providing adequate discrimination?
Example I have a 80amp type c at a 3 phase db which supplies a 3 phase bemco unit which supplies a single phase db to a flat protected by a 63amp fuse.
It's a queer set up an mcb feeding a fuse.
Zs of the cooker circuit is 0.28ohms on a 32 amp type B mcb which is using the nominal voltage calc 821 amps of fault current.
The upstream mcb is a 80amp type c and if you use the tables in bs7671 it will trip at0.1 seconds to 5 seconds with 800amps of fault current so may take out the whole db power.
However I know manufacturers may give different values as bs7671 are generic values across the board.
Also the let through energy may need to be considered for short circuit conditions.
Anyone been down this road before?
 
Last edited by a moderator:
Normally an MCB will not discriminate on fault current from a fuse of similar value.
The manufacturers website normally have discrimination tables that show which values and up to what fault current different devices will provide full or partial discrimination.
However it does tend to be their own products (unsurprisingly) so if you mix manufacturers then you may have a problem.
They should also provide I²t values for their devices.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Discriminating of protective devices from manufacturers
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Ian1981,
Last reply from
Richard Burns,
Replies
1
Views
42

Advert