has anyone ever been in contact with manufacturers regarding providing adequate discrimination?
Example I have a 80amp type c at a 3 phase db which supplies a 3 phase bemco unit which supplies a single phase db to a flat protected by a 63amp fuse.
It's a queer set up an mcb feeding a fuse.
Zs of the cooker circuit is 0.28ohms on a 32 amp type B mcb which is using the nominal voltage calc 821 amps of fault current.
The upstream mcb is a 80amp type c and if you use the tables in bs7671 it will trip at0.1 seconds to 5 seconds with 800amps of fault current so may take out the whole db power.
However I know manufacturers may give different values as bs7671 are generic values across the board.
Also the let through energy may need to be considered for short circuit conditions.
Anyone been down this road before?
Example I have a 80amp type c at a 3 phase db which supplies a 3 phase bemco unit which supplies a single phase db to a flat protected by a 63amp fuse.
It's a queer set up an mcb feeding a fuse.
Zs of the cooker circuit is 0.28ohms on a 32 amp type B mcb which is using the nominal voltage calc 821 amps of fault current.
The upstream mcb is a 80amp type c and if you use the tables in bs7671 it will trip at0.1 seconds to 5 seconds with 800amps of fault current so may take out the whole db power.
However I know manufacturers may give different values as bs7671 are generic values across the board.
Also the let through energy may need to be considered for short circuit conditions.
Anyone been down this road before?