Discuss DIY Advice Needed! in the DIY Electrical Advice area at ElectriciansForums.net

M

Mr.Simple

Hi, firstly I wanted to publish this in the DIY Forum as I am not an electrician, however the DIY forum appears locked and new members cant post there.

So, my problem is trying to interpret an EIC for a neighbour. I will say again I am not en electrician however I do know about electrics, I have a degree in electronic engineering and my neighbour wanted some technical help.

He has just had an extension and this was completed correctly by a NICEIC Domestic Installer and the system tested. ON page 2ofthe NICEIC Domestic installation Certificate, under "Supply Characteristics" is a value for External Earth Fault Loop impedance Ze of 0.35 Ohms (this is a TNCS system, and I think the ma permissible Ze is 035 Ohms). My understanding f Ze is that it measures the impedance of the circuit from the customers from Consumer unit main earth (disconnected from the board) through the suppliers transformer and back along the live to the live side of the main breaker (hope that this is right). If this is correct then it appears to be on the limit but is in tolerance, so everything is ok.

However in the sexton "Particulars of the installation at the origin' there is another box labelled Measured Ze,and this is 0.14 Ohms. Basically I simply don't understand the difference between the two. Furthermore also in the "Supply Characteristics" area is a box called Prospective Fault Current Ipf recorded as 1.8kA Now using Ohm law and assuming the supply is actually 250v (yes I know that Uo is 230v, but isn't that a sop to the EU) 250 divided by 1800 comes out at 0.138 Ohms, which is near enough measured 0.14 Ohms. So where does the vale 0.35 Ohms come from in the Supply Characteristic area?

I also have an earlier Periodic Inspection Report dating from 2004, before the extension and new wiring, which talks about the Ze as being "measured as 0.32 which is close to the supply limit o 0.35, caution advised" (what caution did they expect my neighbour to take?). This is recorded in the "Supply characteristics" of the Periodic Inspection Report with the comment in observations Section.

Can someone please clarify why there are two entries for Ze on the NICEIC Domestic Electrical Installation Certificate and why they should be different.

Many thanks
 
it might just be an error in that he's put the max. recommended value of 0.35 in the box. 0.14 does appear to tie up with the PFC.
 
On the niceic forms i believe the only time you record two Ze values is for a TT system. So sounds to be a mistake.

Can you take a photo of the page and upload?
 
I would tend to agree that the installer in this case could have made a mistake, but for the similar Ze reading on the old report for the original installation. I have attached a copy of the new Cert and old report. The conflicting Ze's are on the certificate about 3/4 across the page in both supply characteristics and Particulars at the origin.
. 2013 03 06 EIC For New Ccts.jpg2004 01 07 Original Periodic.jpg
Also as the new cert is for a consumer unit fed from a breaker in another (old) consumer unit is the Ze measured at the old CU or the new one?
 
Ze is always measured at source. on a 2nd DB ( CU) the term is Zdb.
 
Hi, firstly I wanted to publish this in the DIY Forum as I am not an electrician, however the DIY forum appears locked and new members cant post there.

So, my problem is trying to interpret an EIC for a neighbour. I will say again I am not en electrician however I do know about electrics, I have a degree in electronic engineering and my neighbour wanted some technical help.

He has just had an extension and this was completed correctly by a NICEIC Domestic Installer and the system tested. ON page 2ofthe NICEIC Domestic installation Certificate, under "Supply Characteristics" is a value for External Earth Fault Loop impedance Ze of 0.35 Ohms (this is a TNCS system, and I think the ma permissible Ze is 035 Ohms). My understanding f Ze is that it measures the impedance of the circuit from the customers from Consumer unit main earth (disconnected from the board) through the suppliers transformer and back along the live to the live side of the main breaker (hope that this is right). If this is correct then it appears to be on the limit but is in tolerance, so everything is ok.

However in the sexton "Particulars of the installation at the origin' there is another box labelled Measured Ze,and this is 0.14 Ohms. Basically I simply don't understand the difference between the two.The first box relates to Ze by enquiry,ie...the DNO stated Ze.....the second box is the actual measured Ze. It would be normal practice on an existing install to only fill in the measured Ze,as it is obviously not necessary to ascertain Ze by enquiry. Furthermore also in the "Supply Characteristics" area is a box called Prospective Fault Current Ipf recorded as 1.8kA Now using Ohm law and assuming the supply is actually 250v (yes I know that Uo is 230v, but isn't that a sop to the EU) 250 divided by 1800 comes out at 0.138 Ohms, which is near enough measured 0.14 Ohms. So where does the vale 0.35 Ohms come from in the Supply Characteristic area?

I also have an earlier Periodic Inspection Report dating from 2004, before the extension and new wiring, which talks about the Ze as being "measured as 0.32 which is close to the supply limit o 0.35, caution advised" (what caution did they expect my neighbour to take?). This is recorded in the "Supply characteristics" of the Periodic Inspection Report with the comment in observations Section.

Can someone please clarify why there are two entries for Ze on the NICEIC Domestic Electrical Installation Certificate and why they should be different.

Many thanks

My text in red.
 

Reply to DIY Advice Needed! in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
527
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
994
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock