I have 2 DOL starters which share the same supply for 2 toilet extract fans I have a selector switch wired up and and a set of auxilliary
normally closed contacts on each of the DOL starters to prevent both fans running at the same time. If possible could some one point me please in the direction of a diagram to allow me to wire the fans for automatic changeover in the event of the duty fan tripping out on overload as there is no nanatural ventillation in the toilet core .
I have 2 trip lamps to indicate which fan has tripped and I have wired up the DOL starters for automatic changeover via the overload on the dol starters connections 96 and 97 my problem is the way I have wired it is that if I set fan 1 as duty, the trip lamp on fan 2 is on even though fan 2 has not tripped I know why the lamp is on but I dont have the intelligence to solve the issue that is why I am asking for help from the forum members
Thanks Dimspark
 
It's hard to say what's wrong without seeing your circuit. As I understand it, the indicators are meant to show a tripped condition but instead are just showing that a fan is not running. Therefore I assume they are being controlled by the contactors not the overload relays? You mention terminal 97 - do you have both N/C (95-96) and N/O (97-98) on the overload relay? If so this is fixable. The control feed can go to both overload relays 95 & 97 first. Each 98 controls its trip indicator independently of everything else. Then each 96 feeds one pole of the DP C/O duty selector, which energises the contactor directly when set to duty but via the opposite contactor's N/C interlock contact when set to standby.

Tomorrow I could draw this if unclear. Are there any remote controls / start & stop buttons?
 
Last edited by a moderator:
It's hard to say what's wrong without seeing your circuit. As I understand it, the indicators are meant to show a tripped condition but instead are just showing that a fan is not running. Therefore I assume they are being controlled by the contactors not the overload relays? You mention terminal 97 - do you have both N/C (95-96) and N/O (97-98) on the overload relay? If so this is fixable. The control feed can go to both overload relays 95 & 97 first. Each 98 controls its trip indicator independently of everything else. Then each 96 feeds one pole of the DP C/O duty selector, which energises the contactor directly when set to duty but via the opposite contactor's N/C interlock contact when set to standby.

Tomorrow I could draw this if unclear. Are there any remote controls / start & stop buttons?
 
Thanks Lucien a diagram would be most helpful in the meantime I am going to try and draw out how I have wired the contactors there are no remote buttons
Thanks Dimspark
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cumbernauld
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
DOL Starters Automatic Change Over
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Dimspark,
Last reply from
Dimspark,
Replies
3
Views
1,725

Advert