Is it non compliant to install 240 V downlights to a lighting circuit with no earth when no earth connection is required at the downlight. A client is having his ceiling lowered and wants spots fitting which would be fire rated. Any advice appreciated. thanks
 
the regs state that a cpc should be provided at every accessory even if the accessory does not require a cpc

So you would be best to put the cpc in a wago / connector if your 230v downlights are double insulated
 
the regs state that a cpc should be provided at every accessory even if the accessory does not require a cpc

So you would be best to put the cpc in a wago / connector if your 230v downlights are double insulated
he ain't got a cpc in the cct. generally it is permissible to fit class II fittings to a circuit with no cpc, but it's debatable if you can do this as you are modifying the cct. and should add a cpc, even if you use a single core green/yellow.
 
the regs state that a cpc should be provided at every accessory even if the accessory does not require a cpc

So you would be best to put the cpc in a wago / connector if your 230v downlights are double insulated

Think you misread his post, he has no earth in the lighting circuit and wonders if its ok install double insulated downlighters which dont require an earth anyway.
 
apologies for misreading. As you are modifying the circuit you would be required to ensure that the existing luminaires in the circuit have a cpc if they require so
 
but if the luminaires are class II, does he need to install a cpc? i'm on the fence on this one.
 
telectrix i reckon morally he does. Even if the luminaires are class II he is modifying a circuit which does not have a cpc. Unless all fittings in circuit are class II (which is highly unlikely). If someone gets the 230 tango off of a fitting which aint earthed and they find out that this spark worked on the circuit last week questions will be asked. Also, if the circuit in question contains bathroom lighting you will have to ensure there is RCD protection for the circuit.
 
i would be inclined to agree with that. some silly sod might come along and fit metal fittings/switches. a bugger if the customer won't pay though , and you have to walk away.
 
very true sometimes you have to weigh up do i do the job or walk away but always better to cover your archie and run a green and yellow ane
 

Reply to Down lights install to lighting with no earth in the Australia area at ElectriciansForums.net

Similar Threads

Hi all. Reasonably competant non electrical engineer homeowner here. I have a question for the experts: I recently replaced a horrible...
Replies
8
Views
1K
Hello, Looking for DIY electrical advice. I have 7 x spots, and each are fitted with 1 x T&E connector block fitting [see photo]. In the past...
Replies
3
Views
688
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
475
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
I am installing 9 LED downlights each with an RGB bulb in (i will try attach pictures on them) - anyway I have been told that they need to be...
Replies
4
Views
803

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top