Hi I am a DIYer, but I did have electricians training about 45 years ago. I'm installing LED downlights (IP65) in my upstairs bathroom. I have the loft insulation protectors (domed ones). The problem is that if I asssemble the light fittings as per the instructions the insulation protector dome will not fit over. The connector block fits at 90 degrees to the light fitting which makes the whole thing too wide. The wires have the heatproof insulation and they terminate inside a small plastic box into a small connector block. My question is would it be OK to do away with this small plastic box, which mounts on a metal 90 degree bracket and just use WAGO connectors? Even with LED lights I can imagine the temperature inside the domed protector will get quite warm as there are no holes for any heat to escape (unless I drill some). I can zip tie the T&E so that there is no strain on the joints if I ever need to replace a bulb. Will that be acceptable or do I just need to buy bigger insulation protector boxes? Thanks for any advice.
 
the downlights i use are OK to just fit and pile insulation on top. personally, i'd cut the bloody stuff away so there's none close round or above the fitting/we had a heat loss survey done a couple of years ago. existing 2" between joists against 10" itchy-poo over top. estimated annual saving in gas bill was £22.49.
 
If you have to alter the fitting in any way, then there are a few things to think about.

does the original bracket have connections for the earth, and does it need it for the exposed metal parts. Double insulated, the earth still needs connected through to the next fitting.

if using WAGO or other connectors, it would need to be enclosed in a box.

would altering the fitting void any warranty?

I personally would just move the insulation away as others suggested and not use the protectors.
 
If you have to alter the fitting in any way, then there are a few things to think about.

does the original bracket have connections for the earth, and does it need it for the exposed metal parts. Double insulated, the earth still needs connected through to the next fitting.

if using WAGO or other connectors, it would need to be enclosed in a box.

would altering the fitting void any warranty?

I personally would just move the insulation away as others suggested and not use the protectors.
OK Thanks all. I will move the loft insulation out of the way.
 
You could try these:


Plenty of space inside them for the connectors that typically come with downlights.
Yes that's the sort I should have bought. The round doomed ones don't have enough room inside for the fittings I have. Ta.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Ruitland
Business Name
R & M Graphic Services Ltd

Thread Information

Title
Downlights
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
Metalmangler,
Last reply from
LastManOnline,
Replies
16
Views
3,058

Advert

Back
Top