Discuss Drayton 3 port valve - confirmation of fault? in the Central Heating Systems area at ElectriciansForums.net
A
alanl
Called out to newly installed boiler, using the old Drayton MA1 3 port valve.
When HW is on, CH is also on.
Checked all connections/wiring, all seemed connected correctly.
But, getting voltage at the white cable (HW on) at the valve.
Clearly something wrong there, as there should be no voltage unless CH is calling.
So, long story short, 'HW on' cable was not live when disconnected from valve.
But white wire was live, clearly getting a back-feed from somewhere.
Before I go and order a new actuator, I'd like confirmation that it is likely to be a faulty microswitch on the valve causing this fault, or have I missed something?
Alan.
Yes, that is my point, white is live, when it is not connected to anything.
Checked the feed to white, (disconnected from white) and it is live when calling, dead when not.
So that is correct.
Voltage is getting to white from inside the valve, I suspect a faulty microswitch, or faulty circuit board.
As a follow up, yes, it was a faulty actuator.
I havent had time to take the old one apart yet, but I suspect a faulty microswitch inside it.
Don't forget that if the valve is in the 'manual' position mid position) you will get feed back through the switch if hot water is called for and heating is not.
I've since took it apart, and found the micro switch was jammed down, meaning the CH would always be on when there was power to the valve.
Reply to Drayton 3 port valve - confirmation of fault? in the Central Heating Systems area at ElectriciansForums.net
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Hi I have a heatmiser uh4 wiring centre and a grant vortex combi condensing oil boiler, doing the heat and HW in a small cottage, the room stats...
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...