Hello all. A friend of mine is looking to buy a house and got me to have a cursory look at the electrics for him. One thing seemed a little peculiar but i'm not sure whether or not it'd be deemed unsafe when he gets the EICR certificate done.
The Consumer Unit is a fairly recent looking BG Dual RCD one, with all the relevant labels and warning signs on it. However, it seems at some point, someone has added a separate surface mounted circuit (in trunking) for a Freezer (16A MCB, 2.5mm T&E). Since the board only has two Neutral bars, they've fed the Neutral for the freezer supply directly into the load side of the Main Switch Neutral terminal. Therefore to effectively isolate both poles, you have to turn the Main Switch off.
Ideally, they should've used a High Integrity board but will this be seen an 'improvement reccomended' code or something more drastic?
The Consumer Unit is a fairly recent looking BG Dual RCD one, with all the relevant labels and warning signs on it. However, it seems at some point, someone has added a separate surface mounted circuit (in trunking) for a Freezer (16A MCB, 2.5mm T&E). Since the board only has two Neutral bars, they've fed the Neutral for the freezer supply directly into the load side of the Main Switch Neutral terminal. Therefore to effectively isolate both poles, you have to turn the Main Switch off.
Ideally, they should've used a High Integrity board but will this be seen an 'improvement reccomended' code or something more drastic?