Hello all. A friend of mine is looking to buy a house and got me to have a cursory look at the electrics for him. One thing seemed a little peculiar but i'm not sure whether or not it'd be deemed unsafe when he gets the EICR certificate done.

The Consumer Unit is a fairly recent looking BG Dual RCD one, with all the relevant labels and warning signs on it. However, it seems at some point, someone has added a separate surface mounted circuit (in trunking) for a Freezer (16A MCB, 2.5mm T&E). Since the board only has two Neutral bars, they've fed the Neutral for the freezer supply directly into the load side of the Main Switch Neutral terminal. Therefore to effectively isolate both poles, you have to turn the Main Switch off.

Ideally, they should've used a High Integrity board but will this be seen an 'improvement reccomended' code or something more drastic?
 
Last edited:
so where is the L for this circuit taken from? most recent BG boards are hi-integrity and have 3 N bars.
 
Would be a C3 for me, as to isolate both poles anyway you would need to operate the main switch in the first instance. were there any spare ways on the neutral bar on the side it was fed from?
 
Im with Tel here i use BG all the time and have not come across one with only 2 neutral bars they always have 3 , any chance of a picture so we can advise you better
 
So what you have is main switch with the added 16mm to an MCB then the one RCD then the circuits, then another RCD and the remaining circuits and the Neutral then goes to the neutral out side of the main switch
 
Last edited by a moderator:
I would have given it a c2 with the use of 16mm2, it's not good practice but also it isn't the manufacturers specifications.
Would it come under selection and erection of equipment? Could be way off
 

Reply to Dual RCD Split board with unprotected circuit with N wired into Main Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
296
I've got a dual rcd mk sentry board that I want to inverter into an rcbo board. If I link the two neutral bars from the main switch is this OK to...
Replies
3
Views
1K
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
804
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock