Just done a test on a TT system,and got 150ohms on the rod.But got 0.33 on the cooker circuit.
Am i right in thinking the Zs readings are such due the main bonds bringing the resistances down,never had this before
 
If you have an old lead water or gas meter it could really bring the reading down, bit like having a 500 yard earth rod. Saying that i have never seen it go down that low on one of my jobs.

Edit:- should have said pipe not meter!
 
I have a street up the road from me.

All TT and get Ze readings of 0.24 (that is true ze)

Built them in 1920 - dont know what they used for earth but it works well!

Yhea as TC said no reason why services wouldn't bring that reading down to 0.33
 
I have a street up the road from me.

All TT and get Ze readings of 0.24 (that is true ze)

Built them in 1920 - dont know what they used for earth but it works well!

Yhea as TC said no reason why services wouldn't bring that reading down to 0.33

Are you sure they are still TT's?
I have seen a few properties supplied by overhead lines that are actually TNC-S (PME) supplies.
 
Have you tried to test th Ze at th CU with the main earth disconnected ? yes disconnected this will tell you if you are getting another path ie through the gas water as there may be another property near by that has a good earth and is exporting it to you property but you may find that you can loose it if the gas/water company turn up to lay plastic pipes.
 
I have a street up the road from me.

All TT and get Ze readings of 0.24 (that is true ze)

Built them in 1920 - dont know what they used for earth but it works well!

Yhea as TC said no reason why services wouldn't bring that reading down to 0.33

In the 1920's, Electricians actually knew how to make a good TT system!! lol!!
They would have been using long (9/10 foot) rods too, or even scaffold poles, definitely not these modern 1m twigs..

But as others say, probably a good portion of that low value would be attributed to those old lead pipes, but then that would be the installations Zs value not a Ze value...lol!! Having said that, i can show you TT installations in parts of Essex, that are both very old and relatively new with sub 1ohm values similar to those quoted above... All at the end of the day, depends on soil/ground conditions and how deep the earth rods have been driven...
 
Many farms have very good zs readings as with all the bonded steel buildings, steel grids in floors etc. I have seen lots below 1 ohm.
On demolition of an old military building before, we found a 10x10' earth plate!
 
Electrical Safety Testing always provides unmatched quotation upon request and always prompts in their turnaround time to resolve customers concerns.
 
In the 1920's, Electricians actually knew how to make a good TT system!! lol!!

You're joking right? Most of the villages around here use the same system of 'found old pipe' waked into the ground immediately outside the house. Mine is still there (haven't got a result off it) and I know a few still in service + a few I've removed and they're all rubbish!
 
You're joking right? Most of the villages around here use the same system of 'found old pipe' waked into the ground immediately outside the house. Mine is still there (haven't got a result off it) and I know a few still in service + a few I've removed and they're all rubbish!

No i'm not Joking!! Some of the old village electricians may not have been too clever, but in the main, they knew far more about making a good TT system than most electricians today. Virtually every installation outside of the bigger towns and cities were all TT systems in those days. There standard was below 10 ohms, your standard is below 200 ohms, so you tell me who's systems are ''Rubbish'' ??

Think about it just for a second or two.... Your talking about installations that were made neigh on a 100 years ago!!! Do you honestly expect any domestic TT ground electrode to be still anywhere near 100% serviceable?? One things for certain, there would be very little if anything left of the 1m twigs your using today in a 100 years....
 
No i'm not Joking!! Some of the old village electricians may not have been too clever, but in the main, they knew far more about making a good TT system than most electricians today. Virtually every installation outside of the bigger towns and cities were all TT systems in those days. There standard was below 10 ohms, your standard is below 200 ohms, so you tell me who's systems are ''Rubbish'' ??

Think about it just for a second or two.... Your talking about installations that were made neigh on a 100 years ago!!! Do you honestly expect any domestic TT ground electrode to be still anywhere near 100% serviceable?? One things for certain, there would be very little if anything left of the 1m twigs your using today in a 100 years....

I assumed they were copper once till I took them in with my scrap and they stuck to the bloody magnet!
The state of 3/8" electrodes after just 2 years is pretty bad, rusting nicely especially at ground level, I inspected a couple I disconnected a couple of cabins before, pretty shocking when you think that some permanent buildings rely on them!
On our firm we only use them as temporary stakes for cabins gennys and the like.
 

Reply to earth loop readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
804
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
743
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
655
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
519

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock