Hi there Guys

I am new to the UK and have just a quick question. When your earth loop reading I too high in the UK, can you proceed to do an earth/neutral bond before the consumer main switch or do you have to contact the applicable power utility company?
 
Are you talking about an EFLI reading on a final circuit or the external EFLI (Ze) ?

It is prohibited to alter or tamper with equipment belonging to the DNO or the electricity supplier.
 
Thanks Guys. I was talking about the external loop, however I have established that in the UK the DNO is responsible for that cable and I will just alert them. Yes PEN conductor is illegal after the customer point of control. In SA the DNO stops at the meter in the kiosk outside the property. Therefore you have a cable feeding the installation from the meter to the point of control. Sometimes the earth on this cable deteriorates and a earth/neutral bond is then made in order to restore a proper earth.
 
Thanks Guys. I was talking about the external loop, however I have established that in the UK the DNO is responsible for that cable and I will just alert them. Yes PEN conductor is illegal after the customer point of control. In SA the DNO stops at the meter in the kiosk outside the property. Therefore you have a cable feeding the installation from the meter to the point of control. Sometimes the earth on this cable deteriorates and a earth/neutral bond is then made in order to restore a proper earth.

Even in that scenario it would be unacceptable to make such an earth/neutral link. If the earth conductor has deteriorated then the cable is damaged and must be replaced (or repaired if possible)
 

Reply to Earth Loop too High in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, DIY'er here looking for a bit of advice so please go easy on me. In my dining room there is an existing single pendant and i would like...
Replies
6
Views
459
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K
I have a box powering three 3-phase motors off of one 240V single phase line, NEMA 10-30. In the picture you can see a wiring diagram. The...
Replies
8
Views
1K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
523

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock