Was doing an EICR today and the for the installation was the same size as the tails. 25mm, would this go down as a c3??
Discuss Earth size for installation in the UK Electrical Forum area at ElectriciansForums.net
Is earth not normally half in size'Why?
just past my trade test didn’t realise when you passed you should all of a sudden know everything, I’ll remember this in futureDo you consider yourself competent to do an EICR?
With 25mm² tails you would normally have a 16mm² earthIs earth not normally half in size
No, the earth is not half size of the line and neutral conductors. Where and by whom were you told that was the case? The reason I ask is because if you have course notes or advice in a text book stating this you should be aware that other info you have from the same source could also be tainted or false.Is earth not normally half in size
Well my wife don't, does she? Errr nevermind.oversize is what all women seek
To be fair, knowing an oversized earth is not a problem, is not knowing everything it is just knowing basics. The only problem I could conceive with an oversized earth is a bigger bang when things go wrong.when you passed you should all of a sudden know everything