For years it has been a requirement to bond to metal back boxes with one fixed lug. In 2004 or 2005, an amendment to 16th then said as long as there was 1 fixed lug, the box need not be bonded, reliant on the faceplate pins to provide it's earth. Is this still current under the 17th? One of my concerns is that, when replacing plastic plate switches with metal ones ( brass / stainless ) these faceplates have an earth terminal which must be earthed, so does one take the existing earth off the back box and connect it to the faceplate, or bond from box to plate. it is common practice for decorators to undo sockets and switches so as to paint the wall, not the fitting or get wallpaper behind the faceplates. Obviously, when the screws are out, the box has no earth, so my thoughts are to bond both. CYA. What do my learned friends on here think?
 
Personally I would always take a bond to any metal back box even though there is now no need as stated. As for metallic faceplate I would have both bonded although the regs would only require the plate to be bonded. Good practice IMO.


Sent from my iPhone using Tapatalk
 
it is common practice for decorators to undo sockets and switches so as to paint the wall, not the fitting or get wallpaper behind the faceplates. Obviously, when the screws are out, the box has no earth, so my thoughts are to bond both.

It is not the responsibility of the regs to safegaurd the decorator who decides to interfere with a live installation
He should isolate the equipment before removing,no different to ours, or anybody elses responsibility
The regs as they stand will give protection to the decorator who doesn't interfere,so they are sufficient, as is

In the real world though,the decorator will do as stated
If the cpc is taken to the faceplate of a class 1 item and a tail returned to the back box,we are then giving protection over and above whats required,that protection will be better than the regs, and will protectr the decorator from his naughty practices :)
 
that was my point entirely. from the decorator's point of view, he can't decorate in the winter afternoons with the lights isolated. This is why I myself prefer to bond the boxes. "Think of the worst and the worst will happen"
 
I always link the earth to the back box from the plate. Have always done it and find it impossible to break the habit after all these years of doing it despite what the regs say
 
Never have and Never will.....havent got time....not required. However i always do supplementary bonding in kitchens and bathrooms,and of boilers...even if not required by 17th edition! and that takes a lot longer!! Old habits and all that.....
 
Never have and Never will.....havent got time....not required. However i always do supplementary bonding in kitchens and bathrooms,and of boilers...even if not required by 17th edition! and that takes a lot longer!! Old habits and all that.....

Obviously more money to be made carrying out unnecessary bonding unless you do it for free:(:confused:, otherwise I don't understand the first part of your post when you will spend so much time doing the bonding in the kitchen and bathroom
 
Never have and Never will.....havent got time....not required. However i always do supplementary bonding in kitchens and bathrooms,and of boilers...even if not required by 17th edition! and that takes a lot longer!! Old habits and all that.....

Care to explain why you consider it worthwhile wasting your time and your customers money carrying out unnesessary bonding in the kitchen and of boiler.....whats the thinking?....so the "pipes dont come live"?
 

Reply to Earthing Back Boxes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
878
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
575
I collect old Electrical Fittings and I recently acquired this vintage Junction Box (photos attached). I've been trying to figure out how it would...
Replies
4
Views
711
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
I'm installing smart modules in my light switches which means I need to replace the existing 25mm back boxes with 47mm ones. Downstairs all walls...
Replies
0
Views
316

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock