Discuss Earthing responsibility in the UK Electrical Forum area at ElectriciansForums.net
Hi all,
Holiday village, brick built lodges circa 1960s. Supply is 35mm 4 core armoured, each phase and n comes in to Henley blocks and out to next unit, armour in/out terminated onto metal plate that also has a connection for earth to local consumer unit in each bungalow/cabin. 1 phase used in each unit into a sub meter (unit owner pays the site owner for electric used) then up to CU. No access to where the supply comes from.
So I am calling it TNS… views?
The Ze is 1.08 ohms ZeDB is 1.04 (previously Ze 0.51 on 2017 eicr) ... I notify the owner, but not DNO as surely it is a sub main, so site owners responsibility?
am I missing something?? Surely should be less than 0.8 ohms and the change is of concern anyway… what would you do? thanks all.
I've been confused by this arrangement myself before.
The cable coming into the property/properties is best thought of as a distribution circuit, the earth conductor being a CPC.
You can't know where you stand with Zs until you know the protective device used upstream. For example, that value is within the 5s distribution circuit time of a 32 amp BS88 fuse.
Assuming a TN system, there's certainly not a lot of 'headroom' left for final circuits rated at B32 or above, so I'd agree this needs checking out carefully.
It is suspicious that the measured Ze is much higher now.
If it were still at 0.51 ohm then it is fine for 5s on a 60A supply fuse. At over an ohm it is not leaving much margin if disconnection on OCPD is needed and if the various houses have older installations that might well be the case.
Any idea how long this sub-main is? Are all of the Ze values suspiciously high suggesting some issue at the supply end, rather than some joint point between buildings?
Reply to Earthing responsibility in the UK Electrical Forum area at ElectriciansForums.net
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
5K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
I’m installing 20KW of Solar on my Barn roof, The barn is fed from a 3 phase supply originating at the house which is 80 meters away. I’ll be...