Hi
Saw a mates job the other day where the supply is three phase, however there was two earthing system at head there was tn c s and tn s. So there was separate earth clamped on supply wire to main earth terminal and a additional earth wire run which was connected to neutral of supply ?
Didn't think this is normal practice although dno have recently been to replace fuse ?
Then consumer was wired one earth in earth terminal and the other earth in neutral ?
thanks for replies, both the posts make sense, so if tn-c-s was upgraded then there would be two earth wires in terminal of cu ? or both fed to a met and then one wire fed to cu ?
Hi
Possibly hi Z so belt and braces!!!
I would have expected a DNO notice,at the head,to give some details....not always done,but that is taking it,that the supplier did the mod ;)
Reply to Earthing System Advice in the Commercial Electrical Advice area at ElectriciansForums.net
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...