Hi all, it's been a while but been busy in work and setting up my fledgling company I have a question, have a eicr tomorrow on a ground floor ex council flat. Had a look round earlier and can't find the main equipotential bond to the water but it is visible at the met in the db, if the bonding is under 0.05 ohm near the stop clock, with the gas bond disconnected can I class this as a c3? The supply is tt BTW not that it should matter, any advice greatly appreciated
 
You have no way of knowing the conductor at the MET is the water bond. Of course you can check it's continuity but this won't prove much except it has a connection to earth.
You don't own a rusty VW Golf by any chance.
 
Haha, I own a vw polo but far from rusty! I hope you are not implying I'm a cowboy I'm just asking a tricky question, OK so c2
No no it was from a previous thread I posted about seeing this rusty car in Port Talbot and I saw your location.
 
How you Code it is up to you and whether through tests you deem it requiring urgent attention.
 
No, I think you need to carry out some tests and you may find the conductor with a bit more investigation, all this before you decide on a Code.
 
Didn't spot the tt bit. There is every chance that tests would theoretically suggest it is a water bond by disconnecting and reconnecting it.
 
Agreed, just dont want to charge extra to install a bond from the db, although wouldn't be much cost - about 15m cable plus trunking, just been having a mare lately, 2 Rcd faults in a week or so, one a mem board with a functional earth causing probs, as I said a new business, just want to ensure everything is cosher, hanks for all replys
 
Do the EICR and consider remedial costs after and don't be blinded to other matters by proving or disproving the water bond. Me I would get the job done then spend a bit of time on the bond problem.
 
Oh the joys . If you have looked in all the usual hidden places they may have bonded it in a pipe box going to the upstairs flat . Councils do strange things.
I worked in one where all the rewired cables come down the exterior wall cavities back to CU. Circa rewire 1984.
 
With all the sticker we have to put on boards these day i sometimes think a bonding location sticker would be a good idea.
Sometimes people don't even know where there water/gas come in.
Yes i know i could make one myself
 
With all the sticker we have to put on boards these day i sometimes think a bonding location sticker would be a good idea.
Sometimes people don't even know where there water/gas come in.
Yes i know i could make one myself

I agree about the labelling. Would be more use than most of the other labels usually stuck to a board. Here's one I did earlier.
IMG_9185 - Copy.JPG
 
Me too. About 15 years ago I submitted a request to the IEE that this should be a requirement and it was put forward for consideration but I received a letter back stating it wasn't necessary, still got it somewhere.
 
Again thanks for all advice, landlord got no probs with me doing the water bonding, also found a dodgy socket no connection to the earth pin somehow, will complete this before issuing the cert
 
Oh ---- I forgot, the earth to the earth rod is about 10" from the wall, 10mm cable not buried so fine, but an obvious tripping hazard, needs conduit etc but wouldn't a conduit box etc pose more of a tripping hazard? Sorry but everything I see lately seems a mind bending issue
 
I dunno, but been told the builders kicked the cable off previously just looks a bit of a ---- up to me, been OK for the last fifty odd years but if the landlords willing to pay??
 
That gas pipe needs some investigation where it goes through the wall , either the sleeving has been pebble-dashed over, or there is no sleeving.
Either way that cement needs cleaning off the copper.
 
It's the effect of the cement on the gas pipe I was referring too , cement eats away the copper. It may be advisable to mention it to the landlord.
If it has been pointed in with cement it is a potential hazard.
 
It's the effect of the cement on the gas pipe I was referring too , cement eats away the copper. It may be advisable to mention it to the landlord.
If it has been pointed in with cement it is a potential hazard.
And this has what to do with an EICR.
 
I dunno, but been told the builders kicked the cable off previously just looks a bit of a **** up to me, been OK for the last fifty odd years but if the landlords willing to pay??
Check Ra / Ze / Zs to see if it's any good. I see it's the skinny rod, so likely just one 1.2m section which may be a bit ordinary. They will have put it out there to clear the building's footings. If you dig - is that the gas line coming up wall there? Have a good look about and go slow.
 
I don't think that connection is very well protected against corrosion, there's no mechanical protection for the cable where it obviously needs it and no means of preventing undue strain on the termination.
Plus it looks like about 6" of the 4' rod is sticking out of the ground, so that's 1/8th of its length not even being used.
 
Like post 3, 17, 26 and 40.
Is this how we have to do things now?
 
Yeah def needs mechanical protection, ze 88 ohms, job today ex council flat bonding everywhere except where it should be, gonna run a ten millimeter on the outside to external gas meter and complete at water incomer, who the hell installs these meters!, they haven't got the foggiest about bonding,, 6 mm clamped to upstairs flat the 10mm to the gas box, ffs mun
 

Reply to Eicr no visible main bond to water services in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just want to know everyone’s approach to testing bonding within houses. I do a lot of EICRs, and I would say more times than not I can never get...
Replies
5
Views
1K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi guys, sorry if this has been asked before. I’m currently in a flat where the tenant queried the water bonding. There’s a 6mm green and yellow...
Replies
4
Views
2K
I have a new combo meter box and 200A main shut off installed outside professionally. It has 4/0 service line coming into it and I have...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock