hi guys
after a little advice,
customer wants an 8.5kw shower fitted to a C.U with a 63a Main Switch. i assume main fuse is 60A. existing circuits Cooker radial 30a mcb, 1 ring main 30a mcb, 1 radial lighting circuit 5 mcb( its a bungalowe )
with diversity applied (quick calculation) 30+5+30+40 x 0.4 = 30
so appears fine but was just reading some literature from Gainsbourgh showers stting that the cu shouls have a minimum rating of 80 amps.
any thoughts