hi guys

after a little advice,

customer wants an 8.5kw shower fitted to a C.U with a 63a Main Switch. i assume main fuse is 60A. existing circuits Cooker radial 30a mcb, 1 ring main 30a mcb, 1 radial lighting circuit 5 mcb( its a bungalowe )

with diversity applied (quick calculation) 30+5+30+40 x 0.4 = 30
so appears fine but was just reading some literature from Gainsbourgh showers stting that the cu shouls have a minimum rating of 80 amps.

any thoughts
 
swap the main switch for a 80A. you are then following manufacturers instructions. if the DNO fuse is sufficiently overloaded to blow (which i doubt) DNO can uprate to 80A or 100A.
 
Is this CU an old BS 3036 rewirable type as that switch sounds like an old BS 5419 type.

If the manufacturers instructions tell you the board must conform to BS EN 60439-3, then I would think about fitting a small shower enclosure seperate from the existing CU.
 
There is no diversity applicable to the first instantaneous water heater (shower), so you will need to uprate the CU main switch if you intend to run the final circuit from there. The shower is a special location so you will need 30mA RCD protection, so a separate shower RCD/MCB CU might be a better solution. However your customer may wish to take this opportunity to have a full 17th ED board change upgrade.
 
Henley block and shower CU would be my suggestion, plus the obligatory look/upgrade of the bonding too!

is it nessacary to split the tails or can i feed a seperate shower cu from the existing spare way in the board

Is this a trick question?

The reason for splitting the tails into Henley blocks is to allow you to fit a separate CU and not interfere with the other consumer and the concern of the main switch ;)

Please be sure to follow the safe isolation procedure in full :thumbsup
 
The reason for splitting the tails into Henley blocks is to allow you to fit a separate CU and not interfere with the other consumer and the concern of the main switch ;)

Please be sure to follow the safe isolation procedure in full :thumbsup

Also it means that the new circuit is protected by a RCD too!
 

Reply to Electric Shower on a 63A Main switch CU in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
842
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
So looking for some help, currently I have a sub mains board in the garage supplied from the house CU on a B16 mcb. Right now the sub mains in the...
Replies
4
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock