This should generate some interesting replies! Good question.

off the top of my head it's mentioned in GN3. I think. Will go and have a look am a bit rusty
 
This should generate some interesting replies! Good question.

off the top of my head it's mentioned in GN3. I think. Will go and have a look am a bit rusty

Lucky Nigel didn't ask you that one then Spartykus! :wink:
 
There is no reg that I know of.
It is mentioned in GN3 in the description of continuity testing. I would suggest that GN8 would have more in depth info regarding bonding though.
 
and what if the bonding conductors are each 10m of 6mm?
 
I had a reading that was 0.5 ohms, and consultant was saying oh that's too high. I was like WTF, are you seriously suggesting that that is not a short circuit? In fact the reading can go much higher and still be a good connection. It's just pure bull.
As nobody can pull any regulation out, just guidance notes, gives me a good argument.
 
I had a reading that was 0.5 ohms,
From where to where?

and consultant was saying oh that's too high. I was like WTF, are you seriously suggesting that that is not a short circuit?
It has nothing to do with short circuit.

In fact the reading can go much higher and still be a good connection.
How do you work that out?

It's just pure bull.
As nobody can pull any regulation out, just guidance notes, gives me a good argument.
It's not a regulation but -

See if you can connect a piece of cable to a pipe and get a reading of more than half an ohm.
 
Mostly I was getting 0.05 ohms, but in this particular area it was 0.5
Consultant said to run a bond from board to pedal stool. I said I would once all the flooring had been completed. Reply was because the floor was incomplete it can become live. Utter bull****.
 
The reading was taken from a wall socket earth to the access floor tile.
I don't really understand that but -

I think everyone assumed, I did, that you were referring to Main Bonding for which the figure of 0.05 ohms is usually quoted.


Mostly I was getting 0.05 ohms, but in this particular area it was 0.5
Consultant said to run a bond from board to pedal stool.
Again, I don't understand.
Is the floor metal?

I said I would once all the flooring had been completed. Reply was because the floor was incomplete it can become live. Utter bull****.
You are probably right.
Bonding is not applied in case the floor (or anything else) becomes live.

If it is a metal floor and you bond it then the reading will be a lot less than 0.5 ohm.
 
In that case, if you are getting 0.5 ohms between socket CPC and floor then it must be bonded somewhere already.

Is he on about supplementary bonding between socket CPC and floor?

Running a main bond from stool to board would be strange.
 
In that case, if you are getting 0.5 ohms between socket CPC and floor then it must be bonded somewhere already.

Is he on about supplementary bonding between socket CPC and floor?

Running a main bond from stool to board would be strange.
its ridiculous, i have come across these floors before.

metal pedestals bolted to floor with metal covered wooden tiles ontop, usually covered with carpet tiles
 
Sorry I was nor clear, we was just taking measurements, no bonds were actually in place. The floor will get an earth via floor boxes.
However we was measuring continuity between wall socket cpc, and tile.
All extraneous earth's were measured.
From uni strut to tray work to trunking to ceiling grid to steelwork etc etc etc.
I was just trying to clarify if there was actually an regulation that stated these measurements should be below 0.05 ohms
 
Sorry I was nor clear, we was just taking measurements, no bonds were actually in place. The floor will get an earth via floor boxes.
However we was measuring continuity between wall socket cpc, and tile.
All extraneous earth's were measured.
From uni strut to tray work to trunking to ceiling grid to steelwork etc etc etc.
I was just trying to clarify if there was actually an regulation that stated these measurements should be below 0.05 ohms
it would be a lot lower from unistrut etc to it.

it will probably only have 2.5/4mm cpc at most.


there was so many glanded swa and steel in last plantroom the cpc reading was a lot lower than L-N because of parralel paths etc
 

Reply to Extraneous bonds values in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

If extraneous structural steel is not exposed does it still require bonding Thanks
Replies
3
Views
640
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
419
OLDBOY
O
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
972

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock