How did the metal flooring grid become extraneous in the first place??

I think there is some confusion here between earthing and bonding. Earthing is generally required with metalwork that forms part of an electrical installation such as metal containment systems (conduit, trunking, tray etc) or where part of an electrical installation is integrated into a metal structure etc (such as in this case, these floor sockets in the metal flooring system)... Other building metalwork that brings an extraneous potential into a building is required to be main bonded. Other building metal work that is not extraneous (proven by testing >22k ohms) needs neither bonding or earthing in fact it could well be dangerous to do so!!
 
Thanks Engineer54. I knew I could rely on you.

The main bonds were indeed to the main steelwork, and ductwork.
A couple of low noise earth's were installed to the server room as would be expected.
It's just that the consultant was insisting on this low continuity reading between points.
Thus the original question.
 
As nobody can pull any regulation out, just guidance notes

A misunderstanding of the Guidance Notes at that. It is suggesting that would confirm continuity between two points. It is NOT suggesting that the resistance of the main protective bonding conductor should not exceed this.
 
A misunderstanding of the Guidance Notes at that. It is suggesting that would confirm continuity between two points. It is NOT suggesting that the resistance of the main protective bonding conductor should not exceed this.

Unless of course the contract electrical specification calls for this as a maximum value. Otherwise you are correct...
 
The 0.05 figure is just the value that is acceptable for a connection. So if you fit an earth clamp to a copper pipe, the value between the conductor connected to the clamp terminal and the pipe it's connected to should be no more than 0.05ohms. It's to confirm the connection is good. If you had a 70m run of 10sq.mm, it's not going to measure 0.05 ohms end to end is it.
 
The 0.05 figure is just the value that is acceptable for a connection. So if you fit an earth clamp to a copper pipe, the value between the conductor connected to the clamp terminal and the pipe it's connected to should be no more than 0.05ohms. It's to confirm the connection is good. If you had a 70m run of 10sq.mm, it's not going to measure 0.05 ohms end to end is it.
https://www.youtube.com/watch?v=rnvNfI__kYU

There is a thought/recommendation that if you earth conductor is more than 25meters in length the you could up the csa from 20mm to 16mm (see link)
 
It's strange that he doesn't say why.


Also, the extraneous-c-p is the pipe which comes out of the ground, not where it is bonded, but that's another story.
 
It's strange that he doesn't say why.


Also, the extraneous-c-p is the pipe which comes out of the ground, not where it is bonded, but that's another story.

He is testing from the pipe as opposed to the clamp to prove he has a decent connection, your 1st point imo he is saying that increasing the csa of the cable will reduce the resistance, don't think there is anything written down, I believe its just a recomendation
 

Reply to Extraneous bonds values in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

If extraneous structural steel is not exposed does it still require bonding Thanks
Replies
3
Views
664
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
447
OLDBOY
O
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock