How did the metal flooring grid become extraneous in the first place??
I think there is some confusion here between earthing and bonding. Earthing is generally required with metalwork that forms part of an electrical installation such as metal containment systems (conduit, trunking, tray etc) or where part of an electrical installation is integrated into a metal structure etc (such as in this case, these floor sockets in the metal flooring system)... Other building metalwork that brings an extraneous potential into a building is required to be main bonded. Other building metal work that is not extraneous (proven by testing >22k ohms) needs neither bonding or earthing in fact it could well be dangerous to do so!!
I think there is some confusion here between earthing and bonding. Earthing is generally required with metalwork that forms part of an electrical installation such as metal containment systems (conduit, trunking, tray etc) or where part of an electrical installation is integrated into a metal structure etc (such as in this case, these floor sockets in the metal flooring system)... Other building metalwork that brings an extraneous potential into a building is required to be main bonded. Other building metal work that is not extraneous (proven by testing >22k ohms) needs neither bonding or earthing in fact it could well be dangerous to do so!!